My 2 cents: if you choose to design and submit per the PE's criteria, insert a prominent note on your drawing indicating the design is per such-and-such drawing stamped by so-and-so PE. Be as specific as possible (sheet #'s, PE's name, state of license, etc). Complete the note by stating the design doesn't meet NFPA 13 requirements. It's not fool-proof, it's not bullet-proof, but the more CYA, the better.
Ed Kramer Lawrence, KS > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Bob > Sent: Thursday, July 25, 2013 1:06 PM > To: [email protected] > Subject: RE: BK Design > > Here is what I expect out of this one. The design is submitted as > indicated, but the AHJ says, "what were you thinking"? The FSC says, > "We did what the PE said to do", AHJ says, "good for you, make it > right". I will submit the PE proto drawing along with the design for > conformation. > Change order in the making. > > Bob Knight, CET III > 208-318-3057 > www.firebyknight.com > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of > Cliff Whitfield > Sent: Thursday, July 25, 2013 12:01 PM > To: [email protected] > Subject: RE: BK Design > > Bob, > > I guess like everything else at BK - You can have it your way! > > Personally, I'd run from that one. > > Cliff Whitfield, SET > President > Fire Design, Inc. > Ph: 719-488-3479 > > > > [email protected] > www.fire-design.com > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Bob > Sent: Thursday, July 25, 2013 11:58 AM > To: [email protected] > Subject: BK Design > > I'm working on a Burger King. I've never done a BK before, so what I'm > about to describe seems ridiculous. > The design criteria is based on a PE proto type from 1978. This is what > the contractor was given and told to use as "spec". > There are combustible concealed spaces above ceilings throughout > premises, but no sprinkler protection is to be provided. The design > criteria is 6 sprinklers over 653 sf in the dining area. To be calc'ed > light hazard. > That's it. Has anyone out here in forum land provided the system for a > BK lately? What was required/done? > > Thanks, > > Bob Knight, CET III > 208-318-3057 > www.firebyknight.com > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum- > firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum- > firesprinkler.org > ----- > No virus found in this message. > Checked by AVG - www.avg.com > Version: 2013.0.3349 / Virus Database: 3209/6518 - Release Date: > 07/24/13 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum- > firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org