Well, it took me 90 seconds to be wrong. BK has long installed sprinklers in every stand alone restaurant. If building code or sprinkler code required, they do full system per NFPA 13. If not they install a less than 13 intended to provide protection below the ceiling. Goal is to improve exiting, and control many fires, though less than a 13 system.
I've even seen an FDC on one of these at a drive through. Why I don't know. bv Smaller portions? I'd guess I am not the only one on the forum who does not need a large portion. Both BK and McD still sell a single burger, even if it is not on the drive-thru reader board. You just have to ask for it. ~250 calories. About what I need for a lunch. ----- Original Message ----- From: "Craig Prahl " <Craig. Prahl @ch2m.com> To: sprinklerforum @lists. firesprinkler .org Sent: Thursday, July 25, 2013 11:23:50 AM Subject: RE: BK Design Of the recent stores around here that I've seen, they are fully protected, dining and kitchen areas, hoods over cooking equipment with internal suppression in the hoods and exhaust duct. Craig L. Prahl , CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg , SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 craig . prahl @ch2m.com -----Original Message----- From: sprinklerforum -bounces@lists. firesprinkler .org [ mailto : sprinklerforum -bounces@lists. firesprinkler .org] On Behalf Of Bob Sent: Thursday, July 25, 2013 2:21 PM To: sprinklerforum @lists. firesprinkler .org Subject: RE: BK Design Good info, thanks Bill. Bob Knight, CET III 208-318-3057 www . firebyknight .com -----Original Message----- From: sprinklerforum -bounces@lists. firesprinkler .org [ mailto : sprinklerforum -bounces@lists. firesprinkler .org] On Behalf Of Bill Brooks Sent: Thursday, July 25, 2013 12:20 PM To: sprinklerforum @lists. firesprinkler .org Subject: RE: BK Design Perhaps a non-required system if bldg fire area < 5000 or < 100 person occupant loading (2012 IBC 903.2.1.2). Then 901.2 Exception would say a system is permitted to be installed for partial or complete protection "provided that such system meets the requirements of this code". I'd say a letter to the contractor would be the next step, referring to the code sections above. "Meets the requirements" could be broadly interpreted to mean sprinklering only a part of the building, selecting materials per NFPA 13, spacing heads per NFPA 13, or some other selection of requirements from NFPA 13. Bill Brooks -----Original Message----- From: sprinklerforum -bounces@lists. firesprinkler .org [ mailto : sprinklerforum -bounces@lists. firesprinkler .org] On Behalf Of Bob Sent: Thursday, July 25, 2013 1:58 PM To: sprinklerforum @lists. firesprinkler .org Subject: BK Design I'm working on a Burger King. I've never done a BK before, so what I'm about to describe seems ridiculous. The design criteria is based on a PE proto type from 1978. This is what the contractor was given and told to use as "spec". There are combustible concealed spaces above ceilings throughout premises, but no sprinkler protection is to be provided. The design criteria is 6 sprinklers over 653 sf in the dining area. To be calc'ed light hazard. That's it. Has anyone out here in forum land provided the system for a BK lately? What was required/done? Thanks, Bob Knight, CET III 208-318-3057 www . firebyknight .com _______________________________________________ Sprinklerforum mailing list Sprinklerforum @lists. firesprinkler .org http ://lists. firesprinkler .org/ listinfo . cgi / sprinklerforum - firesprinkler .org _______________________________________________ Sprinklerforum mailing list Sprinklerforum @lists. firesprinkler .org http ://lists. firesprinkler .org/ listinfo . cgi / sprinklerforum - firesprinkler .org ----- No virus found in this message. Checked by AVG - www .avg.com Version: 2013.0.3349 / Virus Database: 3209/6518 - Release Date: 07/24/13 _______________________________________________ Sprinklerforum mailing list Sprinklerforum @lists. firesprinkler .org http ://lists. firesprinkler .org/ listinfo . cgi / sprinklerforum - firesprinkler .org _______________________________________________ Sprinklerforum mailing list Sprinklerforum @lists. firesprinkler .org http ://lists. firesprinkler .org/ listinfo . cgi / sprinklerforum - firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org