As a contractor I would send an RFI to the Architect and go from there. 
I would not argue with the owner about installing a system in their building. 


Sent from my iPhone

On Jul 26, 2013, at 12:57 PM, "Bill Brooks" <[email protected]> wrote:

> Wouldn't 634 sq ft be partial?
> 
> Bill Brooks
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Cahill,
> Christopher
> Sent: Friday, July 26, 2013 12:03 PM
> To: [email protected]
> Subject: RE: BK Design
> 
> Trying to figure out if you are disagreeing with Curtis other than the
> reference to latest code.  You are right you follow the code in effect as to
> whether you need sprinklers.  So there are differences in which edition in
> whether they are required.  But if not required and you choose to go over
> and above you are still obligated to follow the referenced standard (and
> year) of the adopted code.  See IFC 2006 (and '03 and I still think it's in
> '12) 901.4.2 Nonrequired fire protection systems. Any fire protection system
> or portion thereof not required by this code or the International Building
> Code shall be allowed to be furnished for partial or complete protection
> provided such installed system meets the requirements of this code and the
> International Building Code.
> 
> So you can't do a 634 sq ft system. Now there is a question about doing
> above the ceiling with the phrase for partial...but generally AHJ's rule
> either all of 13 or no sprinkler (when allowed to be non-sprinklered).
> Could one say they are doing a full 13 design below the ceiling or I suppose
> the same question is if you only do 634 sq ft in the building then you have
> a 634 sq ft design (notwithstanding the phantom design area if in the '13
> 13).
> 
> Chris Cahill, PE*
> Senior Fire Protection Engineer, Aviation & Facilities Group Burns &
> McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
> 
> Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in:
> MN
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron
> Greenman
> Sent: Friday, July 26, 2013 10:36 AM
> To: [email protected]
> Subject: Re: BK Design
> 
> Curtis,
> 
> You're obligated to design to the current adopted code of the jurisdiction
> which may or may not be the "latest codes and standards." And if this
> building is a stand alone of <5000 sqft, with an occupancy of <100 it
> doesn't need to be sprinklered at all per IBC (see requirements for an A-2
> occupancy). If the applicable building code is IBC 2003 (I think it changed
> in 2006 but maybe 2009--the prior threshold being <12K sqft and <300
> people), or some earlier version, or one of the other model codes from the
> Twentieth Century, or any code amended upon adoption by a state legislature,
> or an amended municipal or county code (acceptable in home rule states), or
> the code adopted in a major city, requirements can be wholly different
> either requiring more or less protection. If BK has chosen to provide what
> is essentially a volunteer life safety type system to provide customers
> added egress protection in case of emergency (pretty standard thinking in A
> and R type occupancies in the late seventies, through the eighties and into
> the early nineties) in an otherwise non-required building I applaud them.
> That it hasn't been revisited by the corporation since 1978 is troubling but
> it's their decision. Personally I feel I'm pretty savvy as to how a fire
> works and what threat I'm exposed to in the dining area of a stand alone
> corporate fast food joint, and don't even give it a second thought as to
> where I sit other than noting where the exits are.
> 
> Now if it's in a strip mall or a high rise or a full mall it's going to be
> fully sprinklered because of the type of building it's in, first and
> foremost because these buildings will already be sprinklered (at least
> relatively new ones), and secondly because it poses a greater exposure
> threat to it's neighbors, not necessarily its customers.
> 
> More prevalent on the fire alarm forum than here is an attitude of' "If a
> little is good, then the most is best." This is eventually self defeating as
> other interests have larger stakes in buildings than fire guys and fire
> protection contractors , and the concept of cost/benefit and diminishing
> returns has to be considered from the customers' point of view. The
> engineers are supposed to be doing this, but while the design/build model is
> prevalent it's incumbent upon the contractors and techs to study up on this
> stuff and incorporate it into their thought processes. I'm not directing
> these comments at you Curtis, even though it was your comment that put me on
> this track, but rather just in general. Nothing makes my head explode more
> than a spec calling for a double-interlock pre-action system covering a
> closet with a single rack of five or six PC type "servers." Not only an
> unnecessary expense in this case but the wrong system, spec'd because
> someone thought if single-action is good double-action must be better. Damn
> it Jim, I'm no accountant but even I know it's cheaper to have off-site
> back-up than amortizing the cost of one of these things. What I do know is I
> wouldn't even put a double-action over a $10M Cray. Wrong system altogether.
> Rant over.
> 
> 
> On Fri, Jul 26, 2013 at 7:09 AM, <[email protected]> wrote:
> 
>> I'm sure that you're quite aware that your obligation is to design and 
>> protect this facility according to the latest codes and standards.
>> The only way that I'm aware that you might justify a 653 s.f. is 
>> through some application of the room design method in this instance.
>> And, of course, the concealed combustible spaces would still need to 
>> be addressed.
>> 
>> BK must have drug some prints out of a closet, blew off the dust, and 
>> said, "Here ya go...all signed and sealed!"  Bottom line is that codes 
>> and standards trump owner "wants" all day long, so satisfy the code and
> CYA.
>> 
>> Curtis Tower
>> Central Fire Protection
>> 
>> -----Original Message-----
>> From: Bob [mailto:[email protected]]
>> Sent: Thursday, July 25, 2013 12:58 PM
>> To: [email protected]
>> Subject: BK Design
>> 
>> I'm working on a Burger King.  I've never done a BK before, so what 
>> I'm about to describe seems ridiculous.
>> The design criteria is based on a PE proto type from 1978.  This is 
>> what the contractor was given and told to use as "spec".
>> There are combustible concealed spaces above ceilings throughout 
>> premises, but no sprinkler protection is to be provided.  The design 
>> criteria is 6 sprinklers over 653 sf in the dining area.  To be calc'ed
> light hazard.
>> That's it.  Has anyone out here in forum land provided the system for 
>> a BK lately?  What was required/done?
>> 
>> Thanks,
>> 
>> Bob Knight, CET III
>> 208-318-3057
>> www.firebyknight.com
>> 
>> 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>> 
> 
> 
> 
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to