-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim
Davidson
Sent: Thursday, July 25, 2013 12:34 PM
To: [email protected]
Subject: RE: BK Design

Bob,

Back in 1978 BK was trying to sprinkler their stores with a modified
sprinkler criteria that they developed to minimize the cost of installation
and not to be installed in accordance with the legal code requirements of
the AHJ, since BK felt that the sprinkler systems were not a required
sprinkler system by code. However in today's code environment all systems
"required" or "not required" need to be installed in accordance with the
legal code. As you can see the prototype spec does not comply with any part
of NFPA 13. 

If BK requires you to provide per BK's specs have your lawyer draft a hold
harmless agreement requiring BK to indemnify you and your firm and design
personal from any legal action resulting from the installation of the
sprinkler designed and installed to BK's specifications. 

The professional engineer who produced the specs is long gone and
probability arguing with George Church and Joe Manning about the
deficiencies in the engineer's specifications.

Have a fire safe day!

Jim 

  

DAVIDSON ASSOCIATES

Fire Protection Engineering     P. O. Box 4010
Code Consultants        Greenville, DE  19807-0010
Medical Gas Systems Engineering (302) 994-9500
        Fax (302) 234-1781

CONFIDENTIALITY
This report and any attachments are confidential and also may be privileged.
If you are not the named recipient, or have otherwise received this report
in error, please destroy the report, notify the sender immediately, and do
not disclose its contents to any other person, use them for any purpose, or
store or copy them in any medium.
Thank you for your cooperation.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob
Sent: Thursday, July 25, 2013 2:01 PM
To: [email protected]
Subject: BK Design

I'm working on a Burger King.  I've never done a BK before, so what I'm
about to describe seems ridiculous.
The design criteria is based on a PE proto type from 1978.  This is what the
contractor was given and told to use as "spec".
There are combustible concealed spaces above ceilings throughout premises,
but no sprinkler protection is to be provided.  The design criteria is 6
sprinklers over 653 sf in the dining area.  To be calc'ed light hazard.
That's it.  Has anyone out here in forum land provided the system for a BK
lately?  What was required/done?

Thanks,

Bob Knight, CET III
208-318-3057
www.firebyknight.com




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
-----
No virus found in this message.