Admittedly, I have not followed much of this thread and some of the emails have been deleted, but let me throw out a couple of thoughts:
1. Is this facility located in an area where the ground freezes? Could we be talking frost heaves? 2. Have any soil samples been taken and analyzed for chemicals? Could something be chemically eating the pipe? Soil based MIC? 3. Are the failures occurring at the joints or in the pipe body? 4. Seismic activity? Fracking? Sink hole potential? 5. Failures occurring in existing pipe at various locations or always at the same location on both new and old? 6. Any other seasonal activity in the area? I apologize if these have been previously addressed, but wanted to throw that out. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com On Aug 19, 2013, at 7:47 AM, "Brad Casterline" <[email protected]> wrote: > Just to add something perhaps non-sensical to all the sensical questions: > could something about the over-head system be playing a part in this? What > are the details of the over-head systems, i.e., wet, dry, grids, trees, 1/2" > pressure relief set at ? PSI, pressures above and below clappers of riser > checks, etc? > > -----Original Message----- > From: Haas, Edward [mailto:[email protected]] > Sent: Saturday, August 17, 2013 10:53 AM > To: [email protected] > Subject: leaky yard mains! > > Yard main around large distribution center exhibits apparently random leaks > every winter into spring. Leaks are excavated and repaired, and yard main > then holds pressure all summer and fall - until the next season. Owner is > tired of repeated impairments, and seeks intelligent solution. Anyone? > Several reliable contractors are stumped. Thank you! > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org