Next questions:  does it have to be 'listed' or just 'approved'?  Does it
have to be 'slow-close'?

Ed Kramer
Lawrence, KS

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Wednesday, September 25, 2013 12:44 PM
To: [email protected]; [email protected]
Subject: RE: Full Forward Flow Test Control Valves

No. 

The building code requires, "All valves controlling the water supply ...
" for automatic sprinkler systems, pumps, tanks, etc. be supervised.   A
test valve is not a fire protection water supply control valve.  


Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg
McGahan
Sent: Wednesday, September 25, 2013 10:34 AM
To: [email protected]
Subject: Full Forward Flow Test Control Valves

Without going back through the rest of the mile long thread.......

IF there is a control valve in the normally closed position for Full Forward
Flow Testing,  is it REQUIRED to be monitored?

Thanks,

--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to