NIBCO and Victauliic do.  Standard industry practice for several years.

John

Sent from my Motorola Smartphone on the Now Network from Sprint!


-----Original message-----
From: Charles Thurston <[email protected]>
To: Dwight Havens <[email protected]>
Sent: Wed, Sep 25, 2013 20:39:45 EDT
Subject: Re: Full Forward Flow Test Control Valves

Hello Dwight,

Actually you can order butterfly valves set to be monitored in the closed 
position, I think Viking is the only one that has them now.

Wednesday, September 25, 2013, 8:20:53 PM, you wrote:

> Even better question, since the switches used to electronically
> supervise sprinkler control valves have to operate within two turns
> of the fully open position, does electronically monitoring a
> normally closed valve do anything for yo, because it only operates
> just before the valve is fully open?

> Dwight




> ________________________________
>  From: "Kramer Design, LLC" <[email protected]>
> To: [email protected]
> Sent: Wednesday, September 25, 2013 2:04 PM
> Subject: RE: Full Forward Flow Test Control Valves
>

> Next questions:  does it have to be 'listed' or just 'approved'?  Does it
> have to be 'slow-close'?

> Ed Kramer
> Lawrence, KS

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve
> Leyton
> Sent: Wednesday, September 25, 2013 12:44 PM
> To: [email protected]; [email protected]
> Subject: RE: Full Forward Flow Test Control Valves

> No.

> The building code requires, "All valves controlling the water supply ...
> " for automatic sprinkler systems, pumps, tanks, etc. be supervised.   A
> test valve is not a fire protection water supply control valve.


> Steve Leyton




> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg
> McGahan
> Sent: Wednesday, September 25, 2013 10:34 AM
> To: [email protected]
> Subject: Full Forward Flow Test Control Valves

> Without going back through the rest of the mile long thread.......

> IF there is a control valve in the normally closed position for Full Forward
> Flow Testing,  is it REQUIRED to be monitored?

> Thanks,

> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Best regards,
 Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to