Look close. I don't have a reference for you. I don't even know if it's
codified in NFPA, but I know best practice is to reverse that rule for
normally closed valves. I also know Victaulic has a butterfly that
initiates a signal when the valve is opened two turns for just such an
application.


On Wed, Sep 25, 2013 at 5:20 PM, Dwight Havens <[email protected]>wrote:

> Even better question, since the switches used to electronically supervise
> sprinkler control valves have to operate within two turns of the fully open
> position, does electronically monitoring a normally closed valve do
> anything for yo, because it only operates just before the valve is fully
> open?
>
> Dwight
>
>
>
>
> ________________________________
>  From: "Kramer Design, LLC" <[email protected]>
> To: [email protected]
> Sent: Wednesday, September 25, 2013 2:04 PM
> Subject: RE: Full Forward Flow Test Control Valves
>
>
> Next questions:  does it have to be 'listed' or just 'approved'?  Does it
> have to be 'slow-close'?
>
> Ed Kramer
> Lawrence, KS
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve
> Leyton
> Sent: Wednesday, September 25, 2013 12:44 PM
> To: [email protected];
> [email protected]
> Subject: RE: Full Forward Flow Test Control Valves
>
> No.
>
> The building code requires, "All valves controlling the water supply ...
> " for automatic sprinkler systems, pumps, tanks, etc. be supervised.   A
> test valve is not a fire protection water supply control valve.
>
>
> Steve Leyton
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg
> McGahan
> Sent: Wednesday, September 25, 2013 10:34 AM
> To: [email protected]
> Subject: Full Forward Flow Test Control Valves
>
> Without going back through the rest of the mile long thread.......
>
> IF there is a control valve in the normally closed position for Full
> Forward
> Flow Testing,  is it REQUIRED to be monitored?
>
> Thanks,
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to