Jeremy,

The 50'-0" pipe rule only applies if the Backflow Preventer has butterfly 
valves attached.  If you are using OS&Y valves, then 4.27.3 applies regarding 
the 10 pipe diameters.

Sincerely
Daniel S. Failla Jr.
Assistant Fire Marshal
Charleston Fire Department
Fire Marshal Division
Preservation Through Prevention

Office - 843 - 724 - 5960
Email: [email protected]

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jeremy 
Frazier
Sent: Wednesday, October 02, 2013 11:52 AM
To: [email protected]
Subject: NFPA 20 (2010) 4.27.3.1

BFp to be installed 50' from the fire pump suction flange (as measured along 
the route of the pipe).  Is this a typo?  What it the reasoning for having such 
a long run of pipe without valves?  In a small fire pump room with a bfp, It 
would seem you would have to do a bunch of zig zags with the pipe just to meet 
this requirement.

 

Jeremy Frazier
Designer 

Cavalier Fire Protection

P:571-931-1004

F:571-931-1010