Charles - The 50' rule applies when butterfly valves are used.

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Charles 
Thurston
Sent: Wednesday, October 02, 2013 1:56 PM
To: Jeremy Frazier
Subject: Re: NFPA 20 (2010) 4.27.3.1

Hello Jeremy,

Set your back-flow vertical, 90 off the top end, Then drop to the pump off the 
bull of the T, Run of the T goes onto the pump bypass. It is easy to get the 10 
pipe diameters in this way. 

Wednesday, October 2, 2013, 11:51:50 AM, you wrote:

> BFp to be installed 50' from the fire pump suction flange (as measured along
> the route of the pipe).  Is this a typo?  What it the reasoning for having
> such a long run of pipe without valves?  In a small fire pump room with a
> bfp, It would seem you would have to do a bunch of zig zags with the pipe
> just to meet this requirement.

>  

> Jeremy Frazier
> Designer 

> Cavalier Fire Protection

> P:571-931-1004

> F:571-931-1010

>  

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


-- 
Best regards,
 Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to