Check the listing of the BFP to see if vertical installation is allowed On Oct 2, 2013 1:56 PM, "Charles Thurston" <[email protected]> wrote:
> Hello Jeremy, > > Set your back-flow vertical, 90 off the top end, Then drop to the pump off > the bull of the T, Run of the T goes onto the pump bypass. It is easy to > get the 10 pipe diameters in this way. > > Wednesday, October 2, 2013, 11:51:50 AM, you wrote: > > > BFp to be installed 50' from the fire pump suction flange (as measured > along > > the route of the pipe). Is this a typo? What it the reasoning for > having > > such a long run of pipe without valves? In a small fire pump room with a > > bfp, It would seem you would have to do a bunch of zig zags with the pipe > > just to meet this requirement. > > > > > > Jeremy Frazier > > Designer > > > Cavalier Fire Protection > > > P:571-931-1004 > > > F:571-931-1010 > > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > -- > Best regards, > Charles mailto:[email protected] > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org