Check the listing of the BFP to see if vertical installation is allowed
On Oct 2, 2013 1:56 PM, "Charles Thurston" <[email protected]> wrote:

> Hello Jeremy,
>
> Set your back-flow vertical, 90 off the top end, Then drop to the pump off
> the bull of the T, Run of the T goes onto the pump bypass. It is easy to
> get the 10 pipe diameters in this way.
>
> Wednesday, October 2, 2013, 11:51:50 AM, you wrote:
>
> > BFp to be installed 50' from the fire pump suction flange (as measured
> along
> > the route of the pipe).  Is this a typo?  What it the reasoning for
> having
> > such a long run of pipe without valves?  In a small fire pump room with a
> > bfp, It would seem you would have to do a bunch of zig zags with the pipe
> > just to meet this requirement.
>
> >
>
> > Jeremy Frazier