David, It is not necessarily a match but may be a starting point. It is the only reference I could find to random piled storage. There could be a lot of different dynamics going on. You have constantly varying heights, going from 25 ft near the middle to almost 0 at the edges. Fire that develops quickly and gets hot in a vertical storage arrangement will be slowed by the angle of repose that gives the pile its shape. Fire could spread quicker going from lower points in the pile to higher than a fire at the high point. Since you will have a lot of air voids in this occupancy, you have to potential for a deep seated fire which will be difficult for sprinklers to protect. I think this is why the demand for the wood chips had a relatively low density over a large area with a long duration.
Sprinklers may not be able to protect this type of occupancy so the goal may be to keep it contained until the fire department can get there and fight it manually. A little pre fire planning could go a long way. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com On Oct 2, 2013, at 8:27 PM, David Bitton <[email protected]> wrote: > Hello Todd, > > I also found no protection criteria for bulk storage of various commodities > other than FM Global's Datasheet 8-27, which applies strictly to piles of > wood chips. Furthermore, the design density and area spelled out in that > datasheet are the same, regardless of the storage height. (0.20/3000 to > 0.2/5000, depending on type of system and temperature rating of the heads). > > I am not convinced that a fire involving the materials stored at the facility > in question would progress in the manner as in a pile of wood chips. > > Thank you for your input. > > David > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Todd - > Work > Sent: Tuesday, October 01, 2013 3:13 AM > To: [email protected] > Subject: Re: Sprinkler protection criteria for bulk storage piles > > I am the one who posted the original question. In my situation, I have a 20 > ft pile of mixed household recycling including cardboard boxes, plastic and > glass bottles and metal cans. Based on a similar pile at this location, I > called it a Class IV commodity. Construction debris is a little different. > Not sure where that would fall. The only reference I could find for "pile" > storage is in FM Global standards for wood chips. They have a moderate > density over a large area. > > Keep in mind that in these type of situations, the goal may be to contain the > fire and send an alarm. Extinguishing would be by the fire department and > probably take a long time to get everything finally out. > > It would be nice to consult the EoR, but there very likely isn't one. > > Todd G Williams, PE > Fire Protection Design/Consulting > Stonington, CT > www.fpdc.com > > On Sep 30, 2013, at 7:56 PM, David Bitton <[email protected]> > wrote: > >> I am looking at a recycling facility for construction debris that has large >> indoor piles for wood, asphalt shingles, etc. Storage height is to 25 ft. >> The existing sprinkler system was designed based on the storage requirements >> for solid-piled/palletized storage of Class III Commodities outlined in NFPA >> 13. I believe that such storage falls outside the scope of this chapter. >> However, I am unable to find any guidance elsewhere to address this storage. >> >> >> >> Does anyone have any additional thoughts about the protection of such piles? >> >> >> >> David Bitton, ing. >> >> Quest Loss Control Services Inc. >> >> Les services de prévention des sinistres Quest inc. >> >> 5100, rue de la Savane, bureau 200 >> >> Montréal, QC H4P 1T8 >> >> (514) 341-4545 >> >> www.questlosscontrol.com >> >> >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org