There is no roof over the dumpster. This is a three story building and the 
dumpster is outside the building at the main floor level. But there is a roof 
overhang, I'm guessing maybe 3 feet wide. 

Tony 

----- Original Message -----
From: "rongreenman ." <[email protected]>
To: [email protected]
Sent: Thursday, October 3, 2013 11:49:56 AM
Subject: Re: Garbage Enclosure

I thought you said there was no roof or canopy in the original description.


On Thu, Oct 3, 2013 at 10:27 AM, Tony Silva <[email protected]> wrote:

> Ron, exactly. It is a dumpster pushed up against the building wall. In
> this case two walls due to the way the wall jogs in an "L" shape. My
> concern is 13 requires sprinklering of roofs and canopies where
> combustibles are stored or handled (NFPA 13, 2002 section 8.14.7.4). Won't
> the intent cover this situation also? No, the location of the dumpster
> can't be changed.
>
> Tony
>
> ----- Original Message -----
> From: "rongreenman ." <[email protected]>
> To: [email protected]
> Sent: Thursday, October 3, 2013 7:50:30 AM
> Subject: Re: Garbage Enclosure
>
> Sounds like a fence surrounding a dumpster pushed up against the side of
> the building on three sides to me. Is it a threat? Fire in a container
> against a concrete wall? Under the intake air opening at the combustible
> dust factory? Death penalty law for burning any garbage, even by accident.
> Seriously, what can be damaged, what exposure threat is there to
> neighboring properties, how would you detect it and at what cost sans roof,
> any rules requiring it (I know, that's the question you're asking Tony),
> can you moc=ve the actual hazard a few feet away, etc.?
>
>
> On Wed, Oct 2, 2013 at 10:42 PM, A.P.Silva <[email protected]> wrote:
>
> > An office building (NFPA 13) has a garbage enclosure outside the
> building,
> > but attached to it. The garbage enclosure has no access from the building
> > It
> > is fenced with gates from outside and does not have a roof.As it is
> > attached
> > to the building, is it required to be sprinklered?
> >
> > Tony
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to