Answer is you don't include them. Section 23.4.4.6.3 ('13 ed)with related
handbook commentary is what you want to look at.


On Tue, Oct 8, 2013 at 8:17 PM, Steven Scandaliato
<[email protected]>wrote:

> Dwight y et al,
> I was waiting for someone to finally bring up this section...everyone needs
> to stop and read this section.  How many of you actually knew this was in
> here?  That’s right....someone actually requested a formal interpretation
> regarding the need for sprinklers under conference tables because why???
> They are over 48"!  Are you kidding me?  The first time I read that back in
> the early 80's I thought long and hard about getting back into beach
> bartending.  I would LOVE to dive head first into this subject....but maybe
> 6 people would care and the rest would lose interest after the first 6
> pages.....As ridiculous as 8.5.5.3.2 sounds, it originated as a response to
> a formal interpretation back in the late 70's.  How it found its way into
> the actual body of the text is because it was a formal
> interpretation...cause God knows none of us would ask such a
> question....right?
>
> Actually is wasn’t the question that killed me, it was the answer.  Instead
> of saying something like, "no,  let's not get carried away" or "no cause we
> don’t think there will ever be enough trash or ignition sources under
> conference tables" they (the committee) came back with "no because its not
> fixed"!  AAAAHHH!  Are you kidding me?   I haven’t seen to many conference
> tables that need to be bolted to the floor to call them fixed, but
> nevertheless there it is...meaning, we are going to start putting sprig-ups
> under conference room tables if they are determined to be "fixed"!
>
>  So is it an exception or just something that gives us a false sense of
> understanding.  For example, because a duct that is 49" wide  and is
> obviously considered "fixed" requires a sprinkler,  the fact that it is
> only
> 24" off the floor in a mechanical room changes things?  This rule is my
> favorite rule...and I could pontificate for hours...I need to settle down
> and go get a glass of red....  For now, I think the appendix for 8.5.5.3.1
> gets us out of this one (overhead doors) and we can move onto something
> else....unless of course you'd like to read 25 pages (not including
> illustrations) of Sicilian rhetoric regarding the "Obstruction Rules for
> Sprinklers; Life With the 4 Foot Rule"....LOL!  Surely we all have better
> things to do...like read the new phone book!
> Ciao,
>
> Steven Scandaliato, SET CFPS
> 520.971.2322 Cell
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Dwight
> Havens
> Sent: Tuesday, October 08, 2013 8:24 PM
> To: [email protected]
> Subject: Re: Sprinklers Below Overhead Doors
>
> But wait...8.5.5.3.1 only applies to fixed obstructions over 4 foot
> wide...8.5.5.3.2 provides an exemption for obstructions that are not fixed,
> such as roll-up doors.
>
> Dwight
>
>
>
>
> ________________________________
>  From: Steven Scandaliato <[email protected]>
> To: [email protected]
> Sent: Monday, October 7, 2013 1:30 PM
> Subject: RE: Sprinklers Below Overhead Doors
>
>
> Wow...just a second....so how big does an obstruction have to be before it
> will affect the operation?  There's only a handful of guys that I would
> classify knowledgeable enough to speculate such a statement. That's a
> pretty
> bold statement to make especially given the number of factors in play
> including and most importantly ceiling height above the opened door...
>
> Let's step back a minute...we have a 4ft rule that has been around since
> parchment paper and we have all swallowed the idea that as long as
> something
> isn't greater than 48" we are all safe, but at 49" people may die and
> buildings may burn down.  Agree or disagree with this untested rule...it is
> what it is.  Now, unknown to many, we now have some modeling and testing
> that is currently being worked over in this cycle to introduce guidance for
> clouds and gaps.  However, until such time as that gets worked over and
> argued about in committee, let's just stick with the 48" rule and leave it
> at that...anything beyond that is pure beer and peanuts.  Let's just say
> sprinklers are required under the doors and yes, you can omit them.
> 23.4.4.6.3.1 and 2.  Hopefully we will have better info next edition.
>
> Steven Scandaliato, SET CFPS
> 520.971.2322 Cell
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Tony
> Silva
> Sent: Monday, October 07, 2013 11:06 AM
> To: [email protected]
> Subject: Re: Sprinklers Below Overhead Doors
>
> Your question leads me to believe that you think only one head will operate
> if the door was up. I don't believe the door will act as a heat collector
> to
> prevent the head at the ceiling from operating. True, the door when raised
> will be an obstruction but the door being up or down won't have much of an
> effect on the operation of the sprinkler heads. So why make a difference in
> the method of calculation?
>
> Tony
>
> ----- Original Message -----
> From: "Mike Hill" <[email protected]>
> To: [email protected]
> Sent: Monday, October 7, 2013 10:32:47 AM
> Subject: Sprinklers Below Overhead Doors
>
> Question: Are sprinklers below overhead doors required to be included in
> hydraulic calculations?
>
> When I first started in the industry, I was told that heads below overhead
> doors were required to be included in the hydraulic calculations. The
> reason
> being, it was a temporary obstruction. The door could be up or down if a
> fire broke out, unlike a large duct which was a permanent obstruction.
>
> I was recently questioned by a FPE as to why I included heads below the
> door
> in a hydraulic calculation. I explained my reasoning to him and he accepted
> it. In his eyes I had proven a more demanding situation than was needed so
> it didn't affect his stamping the plans. Flash forward a few weeks and to a
> different project. I now have a much larger operating area and removing
> these (11) heads from the calculation would help it greatly. I am providing
> protection for a firehouse expansion on a military base. This calculation
> is
> in the apparatus bay. UFC requirements are in effect, ceiling height over
> 20'-0" and it is sloped enough to require the 30% increase. The majority of
> the piping being calculated is existing and to remain as is (if at all
> possible).
>
> Using 2007 Edition of NFPA-13 (only one I have handy at the moment).
> 8.5.5.3.1 Specifically mentions overhead doors need protection below. No
> problem here.
>
> 22.2.2.6.3 Does not mention overhead doors when providing situations where
> sprinklers can be omitted from hydraulic calculations.
>
> The wording in these sections seems to support what my mentors instilled in
> my soft pliable mind all those years ago.
>
> What says the forum?
>
> Mike Hill
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to