I wish I could find my 1936 copy.  That was in there.  Well it went more like 
this...sprinklers are their own trade and shall be installed by only those 
trained and experienced.  AHJ is not a field superintendent and is not expected 
to supervise the work.  OK maybe yours improves with bringing AHJ into the 
knowledgeable.   

Chris Cahill, PE*
Senior Fire Protection Engineer 
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, October 09, 2013 10:31 AM
To: [email protected]
Subject: RE: Sprinklers Below Overhead Doors

As I have remarked before. 1.2.2 ('13) should be amended to "shall require 
knowledgeable and experienced design, installation, plan review and 
enforcement".
Ron F

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steven 
Scandaliato
Sent: Tuesday, October 08, 2013 8:17 PM
To: [email protected]
Subject: RE: Sprinklers Below Overhead Doors

Dwight y et al,
I was waiting for someone to finally bring up this section...everyone needs to 
stop and read this section.  How many of you actually knew this was in here?  
That's right....someone actually requested a formal interpretation regarding 
the need for sprinklers under conference tables because why???
They are over 48"!  Are you kidding me?  The first time I read that back in the 
early 80's I thought long and hard about getting back into beach bartending.  I 
would LOVE to dive head first into this subject....but maybe
6 people would care and the rest would lose interest after the first 6 
pages.....As ridiculous as 8.5.5.3.2 sounds, it originated as a response to a 
formal interpretation back in the late 70's.  How it found its way into the 
actual body of the text is because it was a formal interpretation...cause God 
knows none of us would ask such a
question....right?   

Actually is wasn't the question that killed me, it was the answer.  Instead of 
saying something like, "no,  let's not get carried away" or "no cause we don't 
think there will ever be enough trash or ignition sources under conference 
tables" they (the committee) came back with "no because its not
fixed"!  AAAAHHH!  Are you kidding me?   I haven't seen to many conference
tables that need to be bolted to the floor to call them fixed, but nevertheless 
there it is...meaning, we are going to start putting sprig-ups under conference 
room tables if they are determined to be "fixed"! 

 So is it an exception or just something that gives us a false sense of 
understanding.  For example, because a duct that is 49" wide  and is obviously 
considered "fixed" requires a sprinkler,  the fact that it is only 24" off the 
floor in a mechanical room changes things?  This rule is my favorite rule...and 
I could pontificate for hours...I need to settle down and go get a glass of 
red....  For now, I think the appendix for 8.5.5.3.1 gets us out of this one 
(overhead doors) and we can move onto something else....unless of course you'd 
like to read 25 pages (not including
illustrations) of Sicilian rhetoric regarding the "Obstruction Rules for 
Sprinklers; Life With the 4 Foot Rule"....LOL!  Surely we all have better 
things to do...like read the new phone book!
Ciao,

Steven Scandaliato, SET CFPS
520.971.2322 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dwight 
Havens
Sent: Tuesday, October 08, 2013 8:24 PM
To: [email protected]
Subject: Re: Sprinklers Below Overhead Doors

But wait...8.5.5.3.1 only applies to fixed obstructions over 4 foot
wide...8.5.5.3.2 provides an exemption for obstructions that are not fixed, 
such as roll-up doors.

Dwight




________________________________
 From: Steven Scandaliato <[email protected]>
To: [email protected]
Sent: Monday, October 7, 2013 1:30 PM
Subject: RE: Sprinklers Below Overhead Doors
 

Wow...just a second....so how big does an obstruction have to be before it will 
affect the operation?  There's only a handful of guys that I would classify 
knowledgeable enough to speculate such a statement. That's a pretty bold 
statement to make especially given the number of factors in play including and 
most importantly ceiling height above the opened door...

Let's step back a minute...we have a 4ft rule that has been around since 
parchment paper and we have all swallowed the idea that as long as something 
isn't greater than 48" we are all safe, but at 49" people may die and buildings 
may burn down.  Agree or disagree with this untested rule...it is what it is.  
Now, unknown to many, we now have some modeling and testing that is currently 
being worked over in this cycle to introduce guidance for clouds and gaps.  
However, until such time as that gets worked over and argued about in 
committee, let's just stick with the 48" rule and leave it at that...anything 
beyond that is pure beer and peanuts.  Let's just say sprinklers are required 
under the doors and yes, you can omit them.
23.4.4.6.3.1 and 2.  Hopefully we will have better info next edition.

Steven Scandaliato, SET CFPS
520.971.2322 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tony Silva
Sent: Monday, October 07, 2013 11:06 AM
To: [email protected]
Subject: Re: Sprinklers Below Overhead Doors

Your question leads me to believe that you think only one head will operate if 
the door was up. I don't believe the door will act as a heat collector to 
prevent the head at the ceiling from operating. True, the door when raised will 
be an obstruction but the door being up or down won't have much of an effect on 
the operation of the sprinkler heads. So why make a difference in the method of 
calculation?

Tony  

----- Original Message -----
From: "Mike Hill" <[email protected]>
To: [email protected]
Sent: Monday, October 7, 2013 10:32:47 AM
Subject: Sprinklers Below Overhead Doors

Question: Are sprinklers below overhead doors required to be included in 
hydraulic calculations?

When I first started in the industry, I was told that heads below overhead 
doors were required to be included in the hydraulic calculations. The reason 
being, it was a temporary obstruction. The door could be up or down if a fire 
broke out, unlike a large duct which was a permanent obstruction.

I was recently questioned by a FPE as to why I included heads below the door in 
a hydraulic calculation. I explained my reasoning to him and he accepted it. In 
his eyes I had proven a more demanding situation than was needed so it didn't 
affect his stamping the plans. Flash forward a few weeks and to a different 
project. I now have a much larger operating area and removing these (11) heads 
from the calculation would help it greatly. I am providing protection for a 
firehouse expansion on a military base. This calculation is in the apparatus 
bay. UFC requirements are in effect, ceiling height over 20'-0" and it is 
sloped enough to require the 30% increase. The majority of the piping being 
calculated is existing and to remain as is (if at all possible).

Using 2007 Edition of NFPA-13 (only one I have handy at the moment).
8.5.5.3.1 Specifically mentions overhead doors need protection below. No 
problem here.

22.2.2.6.3 Does not mention overhead doors when providing situations where 
sprinklers can be omitted from hydraulic calculations. 

The wording in these sections seems to support what my mentors instilled in my 
soft pliable mind all those years ago.

What says the forum?

Mike Hill



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to