Mark,
Thank you for the tribute, however, I don't disagree with a single word from Steve. I believe he explained it perfectly. The only caveat he might have didn't address was that restraint, *both* vertical and lateral may be omitted when hanger rods less than 6" long measured from the point of attachment to the structure to the top of the pipe, per 9.3.6.5 (2013 edition). This is similar to the rule allowing omission of lateral bracing when using short rod lengths. That's my opinion only and doesn't represent the position of the Hanging and Bracing committee, or NFPA, or anyone else but me.

Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
http://www.parsleyconsulting.com


On 10/21/2013 1:16 PM, Mark A. Sornsin, P.E. wrote:
We appreciate your effort, Steve - and I know you mean well - but I think we 
still want to hear from Ken on this one...

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Monday, October 21, 2013 11:22 AM
To: [email protected]
Subject: RE: NFPA 13 '10 9.3.6 BL Restraint

Per 2013 NFPA 13, and I'm paraphrasing:   By definition, arm-overs are NOT branchlines.   
Where piping - ANY piping - above a ceiling serves a sprinkler in the pendent position below 
the ceiling, and the pressure at that sprinkler is>100psi, the hanger shall be of a type 
that resists vertical movement.  Where seismic protection is required and the provisions of 
9.3 are to be applied, restraint of branchlines against lateral AND vertical movement.  This 
applies to branch piping but not arm-overs.  The end hanger on an armover may require 
vertical restraint subject to the pressure, but not a lateral restraint.  Branch restraints 
are required at intervals according to tables 9.3.6.4(a) and (b) and may be configured as 
one of the five options in 9.3.6.1.  If using splay wire or a rod-type hanger on a 45° 
angle, the restraint must be within 2' of a hanger that resists vertical movement.  If an 
"arm-over" serves two or more sprinklers, it's not an arm-over.

My two-and-a-half-cents ...


Steve Leyton




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steven 
Scandaliato
Sent: Sunday, October 20, 2013 7:01 PM
To: [email protected]
Subject: RE: NFPA 13 '10 9.3.6 BL Restraint

Wagoner....you need to answer this one...

Steven Scandaliato, SET CFPS
520.971.2322 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack
Sent: Sunday, October 20, 2013 7:09 PM
To: [email protected]
Subject: Re: NFPA 13 '10 9.3.6 BL Restraint

Arm over is defined as pipe supplying a single head - if I remember correctly. 
Restraint is not required for arm overs. So technically not required.

Travis Mack, SET
MFP Design, LLC

Sent from my iPhone

On Oct 20, 2013, at 6:01 PM, "Cahill, Christopher"
<[email protected]>
wrote:
Issue is not about vertical restraint from>100 psi. Well below. This
is
strictly an EQ question.

Chris Cahill, PE*
Senior Fire Protection Engineer
Burns&  McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Dwight Havens
Sent: Sunday, October 20, 2013 6:13 PM
To: [email protected]
Subject: Re: NFPA 13 '10 9.3.6 BL Restraint

pendent heads w/>  100 psi






On Sunday, October 20, 2013 6:44 PM, "[email protected]"
<[email protected]>  wrote:
Isn't the thrust restraint a requirement for systems with pressures in
excess of 100 psi?
----- Original Message -----
From: Ron Greenman [mailto:[email protected]]
Sent: Sunday, October 20, 2013 09:42 PM
To: [email protected]
<[email protected]>
Subject: Re: NFPA 13 '10 9.3.6 BL Restraint

Don't have anything at the moment. Is this eq country? Somewhere
there's
something that requires up thrust restraint at the end of line. I think lateral 
is only required for seismic areas, but I'd need to read the section before I 
made an unequivocal statement. No books in the car.
Sent from my iPhone

On Oct 20, 2013, at 2:08 PM, "Cahill, Christopher"
<[email protected]>
wrote:
Got a code section that connects a length of a BL to a restraint or
the
inverse of what you said, that if it needs a hanger then it needs restraint?
I got one that says it doesn't, 9.3.6.7 Drops and armovers shall not require restraint. 
3.5.3 Arm-Over. A horizontal pipe that extends from the branch line to a single sprinkler 
or a sprinkler above and below a ceiling. I just find it odd I can have a 2" pipe 
100' long serving one head and it doesn't need anything but regular old gravity hangers.  
Or I can't find anything to challenge 9.3.6.7.  My case I have a bunch of 3-8'  1" 
legit armovers.
Contractor didn't install restraint and I think he's right technically.
Chris Cahill, PE*
Senior Fire Protection Engineer
Burns&  McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
rongreenman .
Sent: Sunday, October 20, 2013 2:19 PM
To: [email protected]
Subject: Re: NFPA 13 '10 9.3.6 BL Restraint

Restraint is to avoid upward thrust and side to side thrust, whipping
for Devo fans, at the end of a branch line. If an armover does not
need a  hanger it wouldn't need restraint


On Sun, Oct 20, 2013 at 7:50 AM, Cahill, Christopher
<[email protected]>wrote:

Two questions.

Is there a length of an armover that needs restraint?  Imagine a 12'
armover that only feeds one head.

Can restraint be connected to something other than structure, like a
concrete floor above?

Chris Cahill, PE*
Senior Fire Protection Engineer
Burns&  McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]<mailto:[email protected]>
www.burnsmcd.com<http://www.burnsmcd.com/>

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




_______________________________________________
Sprinklerforum mailing list
[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
k
l
er.org


--
Ron Greenman
Instructor
Fire Protection Engineering Technology Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
l er.org _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
l
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2242 / Virus Database: 3222/6270 - Release Date: 10/21/13




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to