Mark you ignorant slut:

I have been out of my office all day, so this is the first opportunity
I've had to sit thoughtfully at a keyboard.  I sincerely apologize that
yesterday's responses didn't meet your standard of care.  Nonetheless,
I'm glad you feel sated or satiated or salivated or however it is that
you feel.  Feelings are good.   However (and Ken, please feel free to
join if you feel compelled) I am not sure that Tom's answer is complete,
and as such I respectfully demur on a couple of points.   

The concept at work is the different "harmonics" of movement in the
building and the relativity of anchorage.  If mains are braced, lines
restrained and ceilings also rigidly braced to the SAME structural
assembly above, then the likelihood of them moving harmoniously in an
earthquake is high, which reduces and can even eliminate the counter
directional movements such as caused by branch line whiplash.   But
rigidly bracing a ceiling is very expensive and very rarely undertaken,
so in nearly every new building where ceilings are simply laterally
braced and furnished with compression struts, the overhead piping is
going to be moving with the roof or floor above, while the ceiling is
expected to move differentially and/or float between structural
assemblies all potentially moving differentially from one another.  

The ASCE prescriptives are based on the concept of building flexibility
into the interface between overhead piping and ceiling, that interface
being ... arm-overs and drops.   ASCE 7 requires at non-rigidly braced
ceilings that either the oversized annular space, or a swing joint or a
flexible hose connection be provided.   So laterally restraining such
piping is counter-intuitive.  And, as far as "lines in the sand" or the
issue of super long arm-overs, I am not sure that we're done.    

Sprinklers have lagged behind other disciplinary designs for the past 20
years for seismic protection.  Since harmonizing 13 with ASCE 7, we've
joined the 21st Century for sure but as the 2010 and 2013 editions are
adopted, and as more states and AHJ's begin to implement requirements
for seismic protection of building systems, these practices are going to
come as something of a shock for sprinkler contractors and designers.  I
never thought we'd have to be structural engineers, but there are
elements of SE in what we're doing here in CA right now for certain
agencies.   If you look at Ken's slides from the convention (link was
posted yesterday), you'll see at the end an exercise for calculating
what is called "deflection" of an exemplar riser nipple.   It's not
called that in the slides, but that's the force being applied.  There
are forces - deflection and compression - and there is displacement.
ASCE 7 requires that building systems be proven adequately protected
from force and displacement and there are formulas for calculating this
stuff.   The ASCE 7 method (simplified but not short-cut in NFPA 13) for
calculating braces is based on worst-case scenarios; if you were to do
site specific calculations it's even more complicated as you have to
multiply by factors for different kinds of structure, even different
weights of concrete in some cases, and differing seismic force factors
from site to site.   So Ken's exercise is a taste of what may be to
come, as it's sound engineering principal to also take deflection into
account for hangers and braces (that's what the references to net
vertical reaction forces allude to in the standard now).   ASCE 7 has a
formula for calculating the longest allowable distance of hangers, based
on piping weight and the seismic force, and it takes the potential
deflection and displacement of the piping into account in that formula.


I guess the point is that is a systematic, rather than a specifically
elemental approach.  The flexibility of drops, combined with the
rigidity of mains and lines, is what makes it work.  The establishment
of adequate resistance to force in the piping and hangers and sway brace
arms are all important factors in assessing the overall design.

I hope that answers your question(s) ...


My opinion only but I'm not on the committee so the disclaimer is just
to make me sound important,

Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Mark A. Sornsin, P.E.
Sent: Tuesday, October 22, 2013 9:40 AM
To: [email protected]
Subject: RE: NFPA 13 '10 9.3.6 BL Restraint

Tom,

Thank-you for your thoughtful and insightful reply.  It addressed our
question and, therefore, should be a model for all of the Forum -
especially Steve and Ken.

Bottom line is, yes, there are 8 ft. arm-overs that would not require
restraint to meet seismic requirements; and there are 8 ft. branch lines
feeding two sprinklers that would require restraint. It seems to be a
bit of a cross-over in the rules, but ultimately doesn't happen much and
thus isn't considered to be a real problem.

I can't speak for Chris (despite having done so before), but I feel
satiated.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom
Wellen
Sent: Tuesday, October 22, 2013 10:00 AM
To: [email protected]
Subject: Re: NFPA 13 '10 9.3.6 BL Restraint

Mark and Chris,


I'll take a stab at this.  The west coast is still grinding the coffee
beans.

The length of an armorer is not expected to be very long.  The adjacent
branch lines cannot exceed 20 feet apart for extended coverage
sprinklers and 15 ft for standard spray sprinklers.  If the armorer is
over 10 ft long coming off a cross main or branch line, it should be
considered to be piped from the adjacent branch line.  The main
objective is to use less pipe, correct?  Why waste pipe length?

So, if that is the case, the committee is not worried about a line with
a single sprinkler and provided the definition of an armover.  A line
with two or more sprinklers is defined as a branch line where they can
be of considerable length.  The longer the line, the more it will have a
whipping action. Thus, Table 9.6.3.4(a) specifies the spacing needed for
restraints based on the Cp in that area and the pipe size ranging from
26 ft to 53 ft.  An armorer shouldn't whip around so much due to its
short length so restraint is not required.  Can there be instances where
there are long armorers?  Sure, especially if there is a drop from a 40
ft ceiling to a ceiling at an 8 ft level.  9.3.6.7 Drops and armorers
shall not require restraint.  What a mess that would be to restrain a
drop located 32 ft from the ceiling.  Steve commented that ceiling grids
should be rigidly braced.  If not, then the oversized hole for the
sprinkler is necessary in the ceiling to keep the ceiling from bre
aking the fusible element.  Will fusible elements still still break
during an earthquake from the ceiling?  Probably.  The cost benefit of
providing restraints on every drop does not warrant them to be
installed.

NFPA 13 is full "lines in the sand" that we don't know the true history
behind them but it seems mostly just to give a warm fuzzy (i.e. 4 ft
obstruction rule, area limitations of 52,000 sf, etc....) and armorers
and branch lines is just one of them.  It doesn't fit all applications,
but the baseline requirement is established.


Tom Wellen
AFSA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to