> Mark you ignorant slut:
> 
> I have been out of my office all day, so this is the first opportunity
> I've had to sit thoughtfully at a keyboard.  I sincerely apologize that
> yesterday's responses didn't meet your standard of care.  Nonetheless,
> I'm glad you feel sated or satiated or salivated or however it is that
> you feel.  Feelings are good.   However (and Ken, please feel free to
> join if you feel compelled) I am not sure that Tom's answer is complete,
> and as such I respectfully demur on a couple of points.   
> 
> The concept at work is the different "harmonics" of movement in the
> building and the relativity of anchorage.  If mains are braced, lines
> restrained and ceilings also rigidly braced to the SAME structural
> assembly above, then the likelihood of them moving harmoniously in an
> earthquake is high, which reduces and can even eliminate the counter
> directional movements such as caused by branch line whiplash.   But
> rigidly bracing a ceiling is very expensive and very rarely undertaken,
> so in nearly every new building where ceilings are simply laterally
> braced and furnished with compression struts, the overhead piping is
> going to be moving with the roof or floor above, while the ceiling is
> expected to move differentially and/or float between structural
> assemblies all potentially moving differentially from one another.  
> 
> The ASCE prescriptives are based on the concept of building flexibility
> into the interface between overhead piping and ceiling, that interface
> being ... arm-overs and drops.   ASCE 7 requires at non-rigidly braced
> ceilings that either the oversized annular space, or a swing joint or a
> flexible hose connection be provided.   So laterally restraining such
> piping is counter-intuitive.  And, as far as "lines in the sand" or the
> issue of super long arm-overs, I am not sure that we're done.    
> 
> Sprinklers have lagged behind other disciplinary designs for the past 20
> years for seismic protection.  Since harmonizing 13 with ASCE 7, we've
> joined the 21st Century for sure but as the 2010 and 2013 editions are
> adopted, and as more states and AHJ's begin to implement requirements
> for seismic protection of building systems, these practices are going to
> come as something of a shock for sprinkler contractors and designers.  I
> never thought we'd have to be structural engineers, but there are
> elements of SE in what we're doing here in CA right now for certain
> agencies.   If you look at Ken's slides from the convention (link was
> posted yesterday), you'll see at the end an exercise for calculating
> what is called "deflection" of an exemplar riser nipple.   It's not
> called that in the slides, but that's the force being applied.  There
> are forces - deflection and compression - and there is displacement.
> ASCE 7 requires that building systems be proven adequately protected
> from force and displacement and there are formulas for calculating this
> stuff.   The ASCE 7 method (simplified but not short-cut in NFPA 13) for
> calculating braces is based on worst-case scenarios; if you were to do
> site specific calculations it's even more complicated as you have to
> multiply by factors for different kinds of structure, even different
> weights of concrete in some cases, and differing seismic force factors
> from site to site.   So Ken's exercise is a taste of what may be to
> come, as it's sound engineering principal to also take deflection into
> account for hangers and braces (that's what the references to net
> vertical reaction forces allude to in the standard now).   ASCE 7 has a
> formula for calculating the longest allowable distance of hangers, based
> on piping weight and the seismic force, and it takes the potential
> deflection and displacement of the piping into account in that formula.
> 
> 
> I guess the point is that is a systematic, rather than a specifically
> elemental approach.  The flexibility of drops, combined with the
> rigidity of mains and lines, is what makes it work.  The establishment
> of adequate resistance to force in the piping and hangers and sway brace
> arms are all important factors in assessing the overall design.
> 
> I hope that answers your question(s) ...
> 
> 
> My opinion only but I'm not on the committee so the disclaimer is just
> to make me sound important,
> 
> Steve Leyton
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Mark A. Sornsin, P.E.
> Sent: Tuesday, October 22, 2013 9:40 AM
> To: [email protected]
> Subject: RE: NFPA 13 '10 9.3.6 BL Restraint
> 
> Tom,
> 
> Thank-you for your thoughtful and insightful reply.  It addressed our
> question and, therefore, should be a model for all of the Forum -
> especially Steve and Ken.
> 
> Bottom line is, yes, there are 8 ft. arm-overs that would not require
> restraint to meet seismic requirements; and there are 8 ft. branch lines
> feeding two sprinklers that would require restraint. It seems to be a
> bit of a cross-over in the rules, but ultimately doesn't happen much and
> thus isn't considered to be a real problem.
> 
> I can't speak for Chris (despite having done so before), but I feel
> satiated.
> 
> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
> Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
> http://www.kfiengineers.com
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Tom
> Wellen
> Sent: Tuesday, October 22, 2013 10:00 AM
> To: [email protected]
> Subject: Re: NFPA 13 '10 9.3.6 BL Restraint
> 
> Mark and Chris,
> 
> 
> I'll take a stab at this.  The west coast is still grinding the coffee
> beans.
> 
> The length of an armorer is not expected to be very long.  The adjacent
> branch lines cannot exceed 20 feet apart for extended coverage
> sprinklers and 15 ft for standard spray sprinklers.  If the armorer is
> over 10 ft long coming off a cross main or branch line, it should be
> considered to be piped from the adjacent branch line.  The main
> objective is to use less pipe, correct?  Why waste pipe length?
> 
> So, if that is the case, the committee is not worried about a line with
> a single sprinkler and provided the definition of an armover.  A line
> with two or more sprinklers is defined as a branch line where they can
> be of considerable length.  The longer the line, the more it will have a
> whipping action. Thus, Table 9.6.3.4(a) specifies the spacing needed for
> restraints based on the Cp in that area and the pipe size ranging from
> 26 ft to 53 ft.  An armorer shouldn't whip around so much due to its
> short length so restraint is not required.  Can there be instances where
> there are long armorers?  Sure, especially if there is a drop from a 40
> ft ceiling to a ceiling at an 8 ft level.  9.3.6.7 Drops and armorers
> shall not require restraint.  What a mess that would be to restrain a
> drop located 32 ft from the ceiling.  Steve commented that ceiling grids
> should be rigidly braced.  If not, then the oversized hole for the
> sprinkler is necessary in the ceiling to keep the ceiling from bre
> aking the fusible element.  Will fusible elements still still break
> during an earthquake from the ceiling?  Probably.  The cost benefit of
> providing restraints on every drop does not warrant them to be
> installed.
> 
> NFPA 13 is full "lines in the sand" that we don't know the true history
> behind them but it seems mostly just to give a warm fuzzy (i.e. 4 ft
> obstruction rule, area limitations of 52,000 sf, etc....) and armorers
> and branch lines is just one of them.  It doesn't fit all applications,
> but the baseline requirement is established.
> 
> 
> Tom Wellen
> AFSA
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to