Uhhhh ... given that enforcement of 25 in general is almost nil, I would
imagine that's a safe assumption.


Steve Leyton



-----Original Message-----
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rongreenman .
Sent: Tuesday, October 29, 2013 12:19 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Transfer Switch Tests

Does anyone else think that enforcement of this will be spotty at best?


On Tue, Oct 29, 2013 at 8:55 AM, John Denhardt
<jdenha...@stricklandfire.com
> wrote:

> From the 25 - 2014 ROP
>
> 25-187 Log #249 Final Action: Accept in Principle
> (8.3.3.4(3) (New) )
> _______________________________________________________________
> Submitter: John Whitney, Clarke Fire Protection Products, Inc.
> Recommendation: Revise text to add; Verify that pump continues to 
> perform at peak load on the alternate power source for 10 minutes or 
> 30 minutes if alternate power source is a standby generator set.
> Substantiation: During annual tests it is only appropriate that the 
> alternate power source also be tested to assure that circuits and 
> generators be tested to confirm they perform under peak load.
> Committee Meeting Action: Accept in Principle Add peak "horsepower" 
> before "load".
> Verify that pump continues to perform at peak horsepower load on the 
> alternate power source for 10 minutes for a alternate utility or 30 
> minutes if the alternate power source is a standby generator set.
> Committee Statement: Clarifies that a standby generator requires a 30 
> minute test while carrying peak electric motor fire pump horsepower 
> load.
> Number Eligible to Vote: 33
> Ballot Results: Affirmative: 33
>
>
> WOW! - No negative votes!  No comments!
>
>
> John August Denhardt, P.E., FSFPE
> Strickland Fire Protection Incorporated
> 5113 Berwyn Road
> College Park, Maryland 20740
> Office Telephone Number:  301-474-1136 Mobile Telephone Number:  
> 301-343-1457 FIRE SPRINKLERS SAVE LIVES - Can you live without them?
>
>
> -----Original Message-----
> From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark A.
> Sornsin, P.E.
> Sent: Tuesday, October 29, 2013 10:32 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Transfer Switch Tests
>
> All of a sudden, flow meters piped back to suction (or suction tank) 
> look like a good thing - at least when you need to test transfer
switches.
>
> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection 
> Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
> http://www.kfiengineers.com
>
> -----Original Message-----
> From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Tom 
> Duross
> Sent: Monday, October 28, 2013 6:29 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Transfer Switch Tests
>
> Can't be every year, really?
> I think (or hope) that's a misprint because flowing 150% for 30 
> minutes is beyond ridiculous.
> No, there is no other way to put peak load on the driver other than to

> pump.
>
> -----Original Message-----
> From: sprinklerforum-boun...@lists.firesprinkler.org
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
> John Denhardt
> Sent: Monday, October 28, 2013 6:42 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Transfer Switch Tests
>
> Agree every year.  But what about the 30 minutes flowing water.  Is 
> there another way to simulate peak load?
>
> Sent from my Motorola Smartphone on the Now Network from Sprint!
>
>
> -----Original message-----
> From: Tom <ihaveakub...@yahoo.com>
> To: "sprinklerforum@lists.firesprinkler.org"
> <sprinklerforum@lists.firesprinkler.org>
> Sent: Mon, Oct 28, 2013 18:36:03 EDT
> Subject: Re: Transfer Switch Tests
>
> Tom,
>
> Not sure if  you are referring to annual testing (NFPA 25) or 
> acceptance testing (NFPA 20) ? If NFPA 25 I believe the transfer test 
> is required annually not every 3 years.
>
> Tom
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud
service.
> For more information please visit 
> http://www.symanteccloud.com__________________________________________
> ____________________________ 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org