Ditto!!!  If you cannot perform the inspection correctly because the
original was not installed right, then get out your "other" pad and write up
a work order to fix it.  It is up to the owner to decide what to do from
here.  I know this is hard to grasp...we are just a bunch of mechanics
looking at the same car wanting to fix stuff that the last guy did, right or
wrong.  If you want to stay true to the scope, fill out the inspection
forms, make your recommendations and wait by the phone for the owner to
call...

Steven Scandaliato, SET CFPS
520.971.2322 Cell
Skype: steven.scandaliato

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Scott A
Futrell
Sent: Saturday, December 07, 2013 8:08 AM
To: [email protected]
Subject: RE: Main Drain Inspection Test

But, if you are doing an inspection in accordance with NFPA 25, and
according to that document and the Technical Committee it assumes the
original installation to be correct, you shouldn't comment on the incorrect
location of the gauge because that is not in your scope.  Just record the
pressures and move on...

Scott Futrell
 
(763) 425-1001 x12 Office
(612) 759-5556 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
rongreenman .
Sent: Saturday, December 07, 2013 8:54 AM
To: [email protected]
Subject: Re: Main Drain Inspection Test

"The installing contractor told the owner: the pressure gauge is installed
in the wrong place and the system is fine."

The manufacturer told the buyer: the brakes were installed in the wrong
place but the car is fine.

The banker told the customer: the investments were posted in the wrong place
but the his money is fine.

The farmer told the consumer: the poisons were used in the wrong place but
the food is fine.

The doctor told the patient: the pacemaker was installed in the wrong place
but he is fine.

"It's alright M'am. We're musicians."


On Fri, Dec 6, 2013 at 10:42 PM, Forest Wilson Fire Sprinkler Contractor <
[email protected]> wrote:

> I recently inspected a wet sprinkler system.
> It was installed in 1997 and had not been inspected or tested since 
> installation.
> I conducted a main drain test.
> The residual pressure was 30 psi. Static 75.
> According to the hydraulic calc plaque, the residual should be 60.
> The gauge was downstream of the main drain, approx 80 feet of pipe 
> downstream.
>
> I sent a Notice of Impairment to the owner and requested a copy of the 
> Contractors Test Cert to use as a benchmark.
> The installing contractor told the owner: the pressure gauge is 
> installed in the wrong place and the system is fine.
>
> Any thoughts?
>
>
> Forest Wilson
> Fire Sprinkler Contractor
> 937-736-0425
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to