Still use them all the ‎time in Canada, usually Albany 1/3 HP with an automatic 
maintenance switch. I have not seen a retard chamber here in Over 15 years

Sent from my BlackBerry 10 smartphone on the Bell network.
From: Richard Mote
Sent: Friday, January 31, 2014 12:14 PM
To: [email protected]
Reply To: [email protected]
Subject: RE: jockey pump only


They may still be used in Canada, a search turns up adds for several, but all 
the companies are Canadian.

Richard L. Mote
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Friday, January 31, 2014 12:10 PM
To: [email protected]
Subject: RE: jockey pump only

I did not have any major issues with it -it was just the first one I have seen. 
I thought I would check in with the forum and see if it was something that 
should raise a red flag.

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Friday, January 31, 2014 11:03 AM
To: [email protected]
Subject: RE: jockey pump only

More popular back in the '60's.  I've seen a bunch.  I don't think there are 
any codes that address.  What were you thinking would be issues to regulate?  
Certainly never required.  Nothing prohibiting.  No size requirements.  On the 
right side of the BFP I suppose.

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Friday, January 31, 2014 10:57 AM
To: [email protected]
Subject: jockey pump only

I ran across a system where the owner has elected to use a small pump to 
pressurize the system in order to prevent municipal water surges from causing 
false trips on the flow switch. Has anyone seen this before? Are there any 
codes that address something like this?

(not something that we installed, or specified... just found it this way)

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to