Jockey (excess pressure) pumps are used a lot up here north of the 49th parallel. I was easily picked out in a crowd many years ago as a Canadian as I mentioned the use of them for sprinkler trim. They work OK IF you have clean water. They are a curse when using lake water as the fine sediment from the water clogs the pressure switches and other components. Retard chambers are allowed in Canada, it just seems the use of excess pressure pumps is the flavour up here.
Kevin in cold cold cold and snowy Canada Kevin Mowle Bruce Power Tiverton, Ontario -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Richard Mote Sent: Friday, January 31, 2014 12:54 PM To: [email protected] Subject: RE: jockey pump only If I remember right from my years with Star, (1987 - 1993) retard chambers were verboten in Canada. There was actually a Canada trim package available for the alarm valves. Richard L. Mote Rowe Sprinkler Systems, Inc. 7994 Route 522, Suite 1 PO Box 407 Middleburg, PA 17842 P 570-837-7647 F 570-837-6335 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of David Sornsin Sent: Friday, January 31, 2014 12:48 PM To: [email protected] Subject: Re: jockey pump only My guess: They're using more alarm valves with retard chambers up their? Dave Sornsin On Friday, January 31, 2014, Cahill, Christopher <[email protected]> wrote: > OK, now I'm intrigued. What's different in the Dominion of Canada? > (NFPA > 24 reference) > > Chris Cahill, PE* > Associate Fire Protection Engineer > Burns & McDonnell > 8201 Norman Center Drive > Bloomington, MN 55437 > Phone: 952.656.3652 > Fax: 952.229.2923 > [email protected] <javascript:;> > www.burnsmcd.com > > Proud to be one of FORTUNE's 100 Best Companies to Work For > *Registered in: MN > > > > > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Jamey > Prentice > Sent: Friday, January 31, 2014 11:31 AM > To: [email protected] > Subject: Re: jockey pump only > > Still use them all the time in Canada, usually Albany 1/3 HP with an > automatic maintenance switch. I have not seen a retard chamber here in > Over > 15 years > > Sent from my BlackBerry 10 smartphone on the Bell network. > From: Richard Mote > Sent: Friday, January 31, 2014 12:14 PM > To: [email protected] > Reply To: [email protected] > Subject: RE: jockey pump only > > > They may still be used in Canada, a search turns up adds for several, > but all the companies are Canadian. > > Richard L. Mote > Rowe Sprinkler Systems, Inc. > 7994 Route 522, Suite 1 > PO Box 407 > Middleburg, PA 17842 > P 570-837-7647 > F 570-837-6335 > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Matt > Grise > Sent: Friday, January 31, 2014 12:10 PM > To: [email protected] > Subject: RE: jockey pump only > > I did not have any major issues with it -it was just the first one I > have seen. I thought I would check in with the forum and see if it was > something that should raise a red flag. > > Matt Grisé PE*, LEED AP, NICET II > Sales Engineer > Alliance Fire Protection > 130 w 9th Ave. > North Kansas City, MO 64116 > > *Licensed in KS & MO > > 913.888.0647 ph > 913.888.0618 f > 913.927.0222 cell > www. AFPsprink.com > > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Cahill, > Christopher > Sent: Friday, January 31, 2014 11:03 AM > To: [email protected] > Subject: RE: jockey pump only > > More popular back in the '60's. I've seen a bunch. I don't think > there are any codes that address. What were you thinking would be > issues to regulate? Certainly never required. Nothing prohibiting. > No size requirements. On the right side of the BFP I suppose. > > Chris Cahill, PE* > Associate Fire Protection Engineer > Burns & McDonnell > 8201 Norman Center Drive > Bloomington, MN 55437 > Phone: 952.656.3652 > Fax: 952.229.2923 > [email protected] > www.burnsmcd.com > > Proud to be one of FORTUNE's 100 Best Companies to Work For > *Registered > in: MN > > > > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Matt > Grise > Sent: Friday, January 31, 2014 10:57 AM > To: [email protected] > Subject: jockey pump only > > I ran across a system where the owner has elected to use a small pump > to pressurize the system in order to prevent municipal water surges > from causing false trips on the flow switch. Has anyone seen this > before? Are there any codes that address something like this? > > (not something that we installed, or specified... just found it this > way) > > Matt Grisé PE*, LEED AP, NICET II > -- David M. Sornsin Fire Protection Design & Consulting Fargo & Bismarck ND 701.371.0643 [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org