We are having a discussion in our office about sprinkler head coverage with 
sloped piping. If we have an area where the branch lines are spaced 13'-7" 
apart, and the heads on the branch lines are 9'-10" apart on the slope (133.39 
sq. ft./ head). The actual floor coverage is 13'-7" x 8'-0" (108.64 sq. ft./ 
head).
 
We are designing for OH Group II occupancy per NFPA #13 - 2013 (130 sq. ft. / 
head). Section 23.4.4.5.5 says that we design for the projected horizontal 
area, which we assume to mean the actual floor area here. Are we OK with the 
108.64 sq. ft., or does the sloped area of 133.39 cause a problem?
 
Greg Lindholm
Fire Protection Project Manager
Howe Heating & Plumbing, Inc.
                                          