the way to think of it (so that it makes sense) is that max area of coverage as 
determined along the slope is for ACTIVATION and are of coverage for the 
calculation is DISCHARGE on the floor.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Feb 14, 2014, at 6:47 AM, James D. Waite <[email protected]> wrote:

> Sorry, I read that too quickly (icemageddon is getting to me).  Yes the 
> overall spacing of 133 is a problem,  but you're allowed to calculate the 
> smaller square footage.  Area of protection is along the slope, and 
> calculated area is horizontal.
> 
> Jimmy Waite, CET - Design Manager

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to