Sorry, I read that too quickly (icemageddon is getting to me). Yes the overall spacing of 133 is a problem, but you're allowed to calculate the smaller square footage. Area of protection is along the slope, and calculated area is horizontal.
Jimmy Waite, CET - Design Manager Fire & Life Safety America- Raleigh District 7711 Welborn Street, Suite 103 Raleigh, NC 27615 Office: 919-872-3250 Cell: 919-868-3546 Fax: 919-877-5775 www.flsamerica.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of James D. Waite Sent: Friday, February 14, 2014 9:43 AM To: [email protected] Subject: RE: Spacing with sloped piping You're good at 108 sq. ft. Jimmy Waite, CET - Design Manager Fire & Life Safety America- Raleigh District 7711 Welborn Street, Suite 103 Raleigh, NC 27615 Office: 919-872-3250 Cell: 919-868-3546 Fax: 919-877-5775 www.flsamerica.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Gregory Lindholm Sent: Friday, February 14, 2014 9:40 AM To: SprinklerFORUM Subject: Spacing with sloped piping We are having a discussion in our office about sprinkler head coverage with sloped piping. If we have an area where the branch lines are spaced 13'-7" apart, and the heads on the branch lines are 9'-10" apart on the slope (133.39 sq. ft./ head). The actual floor coverage is 13'-7" x 8'-0" (108.64 sq. ft./ head). We are designing for OH Group II occupancy per NFPA #13 - 2013 (130 sq. ft. / head). Section 23.4.4.5.5 says that we design for the projected horizontal area, which we assume to mean the actual floor area here. Are we OK with the 108.64 sq. ft., or does the sloped area of 133.39 cause a problem? Greg Lindholm Fire Protection Project Manager Howe Heating & Plumbing, Inc. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ________________________________ The information contained in this email and any attached documents may contain information that is the confidential property of Fire & Life Safety America, Inc ("FLSA"). Any documents created on any FLSA computer or by any employee in the conduct of FLSA business is work product and owned by FLSA. If the reader of this message is not the intended recipient, or the employee or agent responsible to deliver it to the intended recipient, you are hereby notified that any dissemination, distribution or other use of the contents of this communication is strictly prohibited. If you have this communication in error, please immediately notify the sender and delete this email. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ________________________________ The information contained in this email and any attached documents may contain information that is the confidential property of Fire & Life Safety America, Inc ("FLSA"). Any documents created on any FLSA computer or by any employee in the conduct of FLSA business is work product and owned by FLSA. If the reader of this message is not the intended recipient, or the employee or agent responsible to deliver it to the intended recipient, you are hereby notified that any dissemination, distribution or other use of the contents of this communication is strictly prohibited. If you have this communication in error, please immediately notify the sender and delete this email. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org