You got it Jay. Thank You,
Bob Knight, CET III 208-318-3057 www.Firebyknight.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jay Stough Sent: Tuesday, March 18, 2014 8:59 AM To: Sprinkler Forum Subject: wood trusses I have a building that has wood trusses 18" deep. they are showing a membrane roof on top and drywall on the bottom of the trusses. The suspended ceiling is 18" below the drywall. If I am reading 8.15.1 (2007 edition) correctly, I don't need sprinklers between the drywall and suspended ceiling; but it looks like I need (listed) sprinklers in the trusses since it only mentions solid or composite wood joist in the exceptions. Is this correct? -- *Jay Stough* , SET Tilley Fire Equipment Co. Doylestown, PA _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org