http://www.nfpa.org/~/media/Files/Research/Research%20Foundation/Research%20Foundation%20reports/RFCloudCeilings.pdf


Reed A. Roisum, C.E.T. | Karges-Faulconbridge, Inc. | Fire Protection Designer 
| Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
http://www.kfiengineers.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
rongreenman .
Sent: Thursday, March 20, 2014 1:47 PM
To: [email protected]
Subject: Clouds

Have we figured anything out yet? I got asked today: What if you have a 
non-combustable structure with clouds 16" below the ceiling? Can you just have 
everything drop down under the clouds? Well, uh...yes, but maybe not, well..., 
I don't know for sure. Maybe use obstruction rules...? But, for discharge or 
heat collection? Probably both, but what the hell is a cloud in the book? So 
what do you guys think. Or better yet, what does the book say and where? And 
how did you arrive at that conclusion?

--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to