I keep it simple. Put the deflector at the required height then deal with obstructions. Not sure you can get 16" to work with one level. But if your gaps are wide enough and you can get far enough away to be 4" above go for it as a beam.
If you have clouds at 11" then one level should work. Clouds don't exist. It's just like anything else that might be an obstruction. Chris Cahill, PE* Associate Fire Protection Engineer Burns & McDonnell Phone: 952.656.3652 Fax: 952.229.2923 [email protected] www.burnsmcd.com *Registered in: MN Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of rongreenman . Sent: Thursday, March 20, 2014 1:47 PM To: [email protected] Subject: Clouds Have we figured anything out yet? I got asked today: What if you have a non-combustable structure with clouds 16" below the ceiling? Can you just have everything drop down under the clouds? Well, uh...yes, but maybe not, well..., I don't know for sure. Maybe use obstruction rules...? But, for discharge or heat collection? Probably both, but what the hell is a cloud in the book? So what do you guys think. Or better yet, what does the book say and where? And how did you arrive at that conclusion? -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org