The reason I was asking is that there is a fire at a tire warehouse in 
Torrington, CT (for live streaming video, go to wfsb.com, click on the story 
and there is a link to the video at the bottom). Fortunately, the smoke turned 
from mostly black to mostly white, but they have dumped a lot of water on it. I 
was wondering if the 250 was a reasonable number.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Apr 3, 2014, at 12:58 PM, Tim Frankenberg <[email protected]> 
> wrote:
> 
> A maximum realistic manual hand line flow is 350 GPM. There are some that 
> have proven empirically that 500 can be flowed, that is not realistic to the 
> ordinary operator of an engine and the folks on the nozzle. It works in a 
> more controlled environment, but not the typical fire ground. 
> 
> The "typical" fog nozzle is 250 GPM at 100 psi and with the modern advances 
> in hose technology and materials the old friction losses are a bit less than 
> the old cotton jacket days. The 1 1/8" tip solid stream is 262 GPM at 50 PSI. 
> The real world is plus/minus 10-15% on most hydraulics on the fire ground 
> when you factor in gauge accuracy, actual friction losses, elevation changes 
> and nozzle. 
> 
> If the hose is connected to a master stream, the flow is directly 
> proportional to the length but you could be around 600 GPM max on a 2 1/2" 
> line at 100 feet. 
> 
> Best Regards,
> 
> Tim 
> 
> Tim Frankenberg, CT, CFPS
> Fire Product Manager
> Potter Electric Signal Company, LLC
> 5757 Phantom Drive, Ste. 125
> Hazelwood, MO 63042-2429
> 800-325-3936
> 
> www.pottersignal.com
> 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Tom 
> Wellen
> Sent: Thursday, April 03, 2014 11:42 AM
> To: [email protected]
> Subject: Re: actual hose flow
> 
> Like Steve said, it depends.
> 
> Here is a brochure link that may help.  
> http://www.elkhartbrass.com/files/aa/downloads/catalog/catalog-f2-01-08.pdf
> 
> There's 2.5 in. hose and there are 2.5 in. couplings with 3 in. hose.  All 
> kinds of nozzles from adjustable to smooth bore tips from 1/2 in. to 2 in.  
> The hose and hose monitors we carried had both adjustable nozzles and 
> stackable smooth bore tips.  Then the pump operator may use preset pressures 
> or manual throttles.
> 
> It depends on the fire and yes, it's a wrestling match and not a one man job 
> unless it is the ground monitor.
> 
> 
> Tom
> 
> 
>> On Apr 3, 2014, at 11:20 AM, "Steve Leyton" <[email protected]> 
>> wrote:
>> 
>> Obviously, there are countless situational variables, but I have been 
>> told anecdotally that a 2 1/2" line when used on attack can be used
>> anywhere in the range of 150-400 gpm.   At the high end, it's a
>> wrestling match and only used for outside streams.
>> 
>> SL
>> 
>> 
>> 
>> 
>> 
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of 
>> Todd - Work
>> Sent: Thursday, April 03, 2014 9:18 AM
>> To: [email protected]
>> Subject: actual hose flow
>> 
>> I know we assume a 250 gpm flow for a single fire hose. What is the 
>> actual amount of water that is discharged from a 2-1/2" fire hose in a 
>> fire situation?
>> 
>> Todd G Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> www.fpdc.com
>> 860-535-2080 (ofc)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to