Roland, John and Ron,

Thank you for your insight. Appreciate you taking the time. Very interesting. 
It will be very telling to see what the installation task force comes up with.

Rod at Rapid

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland 
Huggins
Sent: Tuesday, April 08, 2014 11:15 AM
To: [email protected]
Subject: Re: galvanized piping

This does seem to be a transitional time regarding the use of galvanized pipe.  
FM still seems to be of the opinion that there is value to using it.  NFPA 13 
on the other hand is attempting to discourage its use but it's process has 
landed it in the middle of an interesting procedural issue.  In the 2013 ed, 
there was a proposal to change the C-value for galvanized pipe to that of black 
steel.  The concern was corrosion.  The problem is that it wasn't overall 
corrosion (the kind that would impact the hydraulic ability of the pipe).  The 
discussion was focused on localized corrosion leading to very early failure of 
the pipe integrity (pin holes leaks). No information was submitted that 
supported the reduction of the hydraulic benefit. Although I think it is a good 
idea to avoid it's use, the technical basis for changing the C-value is 
missing.  Although I pride myself on not being one of those engineers, this is 
an occasion where the pocket protector wearing, that's not techni
 cal correct personality has emerged.  The decision on not allowing or 
discouraging the use of galvanized pipe is suppose t be made by the 
Installation TC, not the Discharge TC.  Public input's for the 2016 were 
submitted that moved to return the C-value and not allow INTERNALLY galvanized 
pipe for dry/preaction systems.  The PI on c-vale was rejected based on no data 
submitted to support the change.  The other PI's were also rejected with a 
statement of:
The use of galvanized pipe still has value in the design of certain sprinkler 
systems when properly pitched and drained. By banning galvanized pipe from 
systems it may impacted trim pipe for dry systems and the use of galvanized 
piping in exterior environments. 

SO it has value, the trim pipe could be exempted , and the exterior setting is 
a externally coated issue.  There is an Installation task group working on this 
issue so some change is expected (most likely something in the annex indicating 
concern about it's use).  In playing Don Quixote, a comment was submitted on 
the c-value with the same data provided in 2013 but I'm not holding my breath 
on that one.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Apr 8, 2014, at 8:25 AM, Rod DiBona <[email protected]> wrote:

> 
> A general question. Do you still believe that galvanized piping should be 
> used for most dry systems / dry standpipes? The makers of idod pipe say yes. 
> The makers of nitrogen generators say no. I had always thought that it was 
> better and that in GENERAL galvanized would last longer. Over the last few 
> years it seems like the tide has changed and I have read studies that come to 
> different conclusions. I understand there are many variables but thank you 
> for your thoughts.
> 
> Rod at Rapid
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to