HydraCALC has a box you can check on the calculation menu for doing a source 
calc. That brings up a question I have been asking for years. I know from 
direct observation when I was testing sprinklers for Star that increases in 
pressure can materially affect droplet size and distribution pattern. If we 
have a system designed to work a 50 psi @ 250 gpm. What happens to the spray 
pattern and droplet size when the fire department come along and starts pumping 
500gpm @ 100 psi into the system. Part of the reason for the minimum pressure 
requirements for Residential sprinklers is that, that was the minimum pressure 
required to pass all the UL testing. If you do the math the pressure required 
does not always matchup with sqrt of P = Q/K. So what happens to the 
distribution and droplet size when you install residential sprinkler in 
residential portions of a 13 occupancy and give it two or three times the 
minimum starting pressure.


Richard Mote ET
Designer
Rowe Sprinkler Systems, Inc.
PO Box 407
Middleburg, PA 17842
P- 877-324-ROWE
F- 570-937-6335
[email protected]
www.rowesprinkler.com





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Thursday, May 22, 2014 11:09 AM
To: [email protected]; [email protected]
Subject: RE: Area/Density Method and Walls

I think most software can do that.  We've been using FPE for a long while and 
the software has a toggle feature between "Demand" and "Supply" calculations.   
The later being a model of system performance at 0 psi remaining at Source.

SL

 




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Thursday, May 22, 2014 7:38 AM
To: [email protected]; [email protected]
Subject: RE: Area/Density Method and Walls

I don't know if Hydracad or SprinkCad has the same option as HASS but HASS puts 
out a secondary calc called Full Flow.  We looked at this and were a bit 
surprised of the results.  Basically when we calculate a system all we are 
doing is proving that we can achieve the required minimum flow and pressure 
within the hydraulically remote area.  When you're done you end up with a 
comparison of REQUIRED versus AVAILABLE pressure and flow.  AS long as the 
REQUIRED is less than the AVAILABLE all is good.

What you don't see is what actually could be discharged based on the ACTUAL 
pressure and flow.  For example if you have a 250 gpm sprinkler demand with a 
required BOR pressure of 50 psi and the water supply can provide 1000 gpm at 
125 psi, your FULL FLOW conditions will discharge MUCH more than the 250 
minimum required.   

So when there is a robust water supply your LH system can easily discharge 
rates closer to an EH system.   

Also consider the statistical data of most fires being controlled by one to 
three sprinklers and we're calculating more than that so you can see where the 
difference between physics and reality come into play.

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Thursday, May 22, 2014 9:54 AM
To: [email protected]
Subject: RE: Area/Density Method and Walls

"The designed system has little to do with physics or reality."

Roland, I did not want to take your statement out of context completely, 
because I know how much that hurts sometimes, so I did not trim this thread.

I am always trying to quantify things as best I can so here is my shot:

At the time calculations were being accepted into NFPA 13 the 'reality' was 
that pipe scheduled systems had worked for 90 years.
In order for proposed changes to be accepted (then and now I guess) an 
equivalency of some sort had to be shown, and that is where the 'physics'
came in, along these lines: given a certain water supply, what flows will a 
scheduled system produce? Now, for the sake of economy, how much can we beef it 
up here and slim it down there and still get equivalent results; mix a little 
fluid mechanics theory with a lot of water flow measurements and...
BOOM! the density/area curves where born.

So calculated systems using the density/area curves are nothing more than 
reconfigured pipe scheduled systems at their roots.

This is just my current understanding, and if it is mostly correct, it makes 
real and perfect physical sense (to me anyway) ;)

Brad Casterline, SET

ps- I think calcs were a quantum leap in fire sprinkler design, and I think the 
future WILL involve 'fire having something to do with it'.
 

-----Original Message-----
From: Brad Casterline [mailto:[email protected]]
Sent: Wednesday, May 21, 2014 12:12 PM
To: 'Roland Huggins'; 'SprinklerFORUM'
Subject: RE: Area/Density Method and Walls

Three people took NFPA 13 from pipe scheduled to calculated:
Jack Wood, Lin McCool, and Hasu Doshi.
The Density/Area Curves "had nothing to do with fire" according to Hasu, the 
only one of the three still alive.
The calculations were performed to see if they could get mains from 8" to 6"
by making the lines a little bigger and still get the same total flow.
So Chris, if you were pipe scheduling your set-up you would ignore the walls, 
right? So there is your answer.
When I said I would consider any barrier I mean I would see in full color 3D 
the flames and smoke and sprinkler spray of what I think would probably happen, 
but what I would calc and print and walk the 40 feet to where my supervising 
FPE of ~35 years, Hasu Doshi, is, I will have ignored the walls.
Hope that helps Cecil.

Brad Casterline
Designer Member, AFSA

-----Original Message-----
From: Roland Huggins [mailto:[email protected]]
Sent: Wednesday, May 21, 2014 10:41 AM
To: SprinklerFORUM
Subject: Re: Area/Density Method and Walls

Actually a good question.

Generally speaking you ignore the walls (exception the room design of course 
and others like small systems where you simply add additional water to the 
calc).  The designed system has little to do with physics or reality.  I've yet 
to see a pendent sprinkler discharge water in a 10X13 rectangle, the amount of 
water hitting the flow is NOT equal to the assigned density (even IF it did 
flow uniformly throughout the pattern which it doesn't), friction loss through 
fittings is not well accounted for from an academic standpoint, if you move the 
sprinkler an additional 6" off a wall it will greatly increase the required 
pressure but do you think it will really affect the performance, unbounded 
fires do burn in a relative circle but the design as never been based on that 
etc etc.  The reality of the design is that it is a well defined process 
whereby different people get relatively similar results AND IT WORKS to control 
the fire.

As such, for a new design, the approach ensures that a fire located anywhere 
will be controlled by assigning the remote area in the most hydraulically 
demanding location regardless of walls.  When modifying a system, you will not 
find anything that relaxes this conservative approach.  So if you are looking 
for a get out of jail card, get comfortably because you're staying in jail.  
Now as an engineer evaluating a modification, one could challenge the 
conventions of the standard and I believe still have an adequate system.
If one is thinking to avoid lawsuits, don't be an engineer (or contractor for 
that matter).  I know of a case where the building burned down and the control 
valve was known to be closed and RECORDED as such for 6 months before the 
fire.The contractor is still being sued - UFB.

Somewhat what Cecil said with a touch of my opinion that is not I say not 
(think of the big chicken from Looney Tunes Foghorn Leghorn pronouncing
that) to be considered an interpretation for NFPA 13 or any other NFPA standard 
(with a few less THE's).

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On May 20, 2014, at 5:12 PM, Cahill, Christopher <[email protected]>
wrote:

> I can't believe I'm asking this question after all these years.  
> Anyway,
swallowing pride and asking.
> 
> 2010 NFPA 13 strict Density/Area method 11.2.3.2 and 22.4.4.1.1.  
> Great
big room being subdivided. Existing system with a new wall added between heads 
on a BL.  Contractor had to add a head on one side to preserve the existing 
spacing (area) of the heads.  Without head over 130 sq.ft.  I take the 1.2 ^.5 
of the area and get 46.5' required along the BL.  Original system lets say 
calc'd 5 heads on the BL.  But now in the same 46.5' there are 6 heads on the 
BL.  Do I ignore the wall and require a new calc?  What if the wall is rated 1 
hour do I ignore it?
> 
> I looked all over and can't seem to find anything definitive. Room 
> design
is out so not a consideration.  22.4.4.1.1.1 simply says all the heads in the 
46.5'.  I can't find anything that says either to count the wall as a break so 
measure 46.5' from the wall in each direction and still see if there are 5 head 
or ignore it and there are now 6 heads.  I find 11.1.2 that clarifies to extend 
the density or not.  I don't think that's applicable exactly. The question is 
not about whether to extend the density on either side. Let's just say it's all 
OH.
> 
> It gets a little more complex as on the one side of the wall they cut 
> a
head in on the BL but on the other side there is a perpendicular new wall and 
they come off same BL and arm over to two more head so if I ignore the walls 
there are now 8 heads off the 1 BL.
> 
> Prefer a code section or written reference 'cuz this is going to be a 
> big
deal if we ignore the walls.  Ordinarily with unrated walls they are ignored in 
density/area (of course can't find that reference).  I think I'm getting 
tripped up with the rated portion? Or maybe I'm just tired????
> 
> Chris Cahill, PE*
> Associate Fire Protection Engineer
> Burns & McDonnell
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]<mailto:[email protected]>
> www.burnsmcd.com<http://www.burnsmcd.com/>
> *Registered in: MN
> 
> 
> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work 
> For
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to