One too many 'the's at the end of your disclaimer Cecil. Not complaining or 
intending to criticize, I'm just a stickler about some things.
b'rad

> On May 20, 2014, at 9:26 PM, Sprinkler Academy - C Bilbo 
> <[email protected]> wrote:
> 
> Hiya Chris,  (we'll meet face to face some day, right?)
> NFPA 13 is a "prescriptive standard" (for those wondering: a standard that 
> will cover just about any situation within certain parameters, so anyone can 
> apply it).  Which means we follow the rules as written.
> You are doing it right when you use the full 46.5' as the basis along a 
> branchline that crosses rooms.  
> Our trade is based, founded, and entrenched in the ability to apply these 
> rules in this way.  The rules are DEFINITELY too conservative for many 
> situations.  But that is what makes our prescriptive methods so successful.  
> If it is enough for tough situations and too much for others, then we are 
> sure to have the good record that we have created.
> To espouse a view, as has been suggested,  that says to the vast majority of 
> contractors and designers, "Do what feels good." is NOT an appropriate 
> answer. 
> The purpose of the remote area being 20% longer than the square (the square 
> root for an inscribed circular fire...) is to make it more demanding on a 
> single branchline and therefore a more conservative prescriptive system.  
> (See the Academy's free remote area 101 lesson.)
> Chris, I know you to be a fair and firm professional.  There is reason here 
> to maintain and require consistency.  (Give em an inch and.....)
> Stick with the definitions in the IBC/Minn and the NFPA and reality will be 
> grand.
> It should be recognized that the above is my opinion as a member of the NFPA, 
> and has not been processed as a formal interpretation in accordance with the 
> NFPA Regulations Governing Committee Projects and should therefore not be 
> considered, nor relied upon, as the official position of the the NFPA, nor 
> any of their technical committees. 
> 
> Sincerely,
> 
> 
> Cecil Bilbo 
> Academy of Fire Sprinkler Technology
> Champaign, IL
> 217.607.0325
> www.sprinkleracademy.com
> 
> [email protected]
> 
> 
> 
> OUR STUDENTS SAVE LIVES!!
> 
> 
> 
>> From: [email protected]
>> To: [email protected]
>> Date: Tue, 20 May 2014 19:12:41 -0500
>> Subject: Area/Density Method and Walls
>> 
>> I can't believe I'm asking this question after all these years.  Anyway, 
>> swallowing pride and asking.
>> 
>> 2010 NFPA 13 strict Density/Area method 11.2.3.2 and 22.4.4.1.1.  Great big 
>> room being subdivided. Existing system with a new wall added between heads 
>> on a BL.  Contractor had to add a head on one side to preserve the existing 
>> spacing (area) of the heads.  Without head over 130 sq.ft.  I take the 1.2 
>> ^.5 of the area and get 46.5' required along the BL.  Original system lets 
>> say calc'd 5 heads on the BL.  But now in the same 46.5' there are 6 heads 
>> on the BL.  Do I ignore the wall and require a new calc?  What if the wall 
>> is rated 1 hour do I ignore it?
>> 
>> I looked all over and can't seem to find anything definitive. Room design is 
>> out so not a consideration.  22.4.4.1.1.1 simply says all the heads in the 
>> 46.5'.  I can't find anything that says either to count the wall as a break 
>> so measure 46.5' from the wall in each direction and still see if there are 
>> 5 head or ignore it and there are now 6 heads.  I find 11.1.2 that clarifies 
>> to extend the density or not.  I don't think that's applicable exactly. The 
>> question is not about whether to extend the density on either side. Let's 
>> just say it's all OH.
>> 
>> It gets a little more complex as on the one side of the wall they cut a head 
>> in on the BL but on the other side there is a perpendicular new wall and 
>> they come off same BL and arm over to two more head so if I ignore the walls 
>> there are now 8 heads off the 1 BL.
>> 
>> Prefer a code section or written reference 'cuz this is going to be a big 
>> deal if we ignore the walls.  Ordinarily with unrated walls they are ignored 
>> in density/area (of course can't find that reference).  I think I'm getting 
>> tripped up with the rated portion? Or maybe I'm just tired????
>> 
>> Chris Cahill, PE*
>> Associate Fire Protection Engineer
>> Burns & McDonnell
>> Phone:  952.656.3652
>> Fax:  952.229.2923
>> [email protected]<mailto:[email protected]>
>> www.burnsmcd.com<http://www.burnsmcd.com/>
>> *Registered in: MN
>> 
>> 
>> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For
>> 
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>                         
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to