Right on sprinkler brother. I start my 40th year as a Designer at the end of 
this month, and I will attend my first convention next month.
The last time I googled 'average FD Hero response time' I think I got something 
like 11 minutes, and that is why I sleep better at night.

> On May 20, 2014, at 8:11 PM, "Cahill, Christopher" <[email protected]> 
> wrote:
> 
> When all the lawyers are gone! And everything back to Hammurabi is repealed!! 
> I've got things to lose and there are VERY few reasons for me to risk those.  
> 
> Forum, no problem, we're all friends I've never met here, well except for a 
> few. 
> 
> Chris 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Brad Casterline
> Sent: Tuesday, May 20, 2014 8:04 PM
> To: [email protected]
> Subject: Re: Area/Density Method and Walls
> 
> Chris, I hope you meant for this to go to The Forum, not just me so I am 
> trying my hand at re-directing it. 
> Isn't it time we start seeing where semantics might be trying to over-ride 
> physics?
> 
>> On May 20, 2014, at 7:44 PM, "Cahill, Christopher" <[email protected]> 
>> wrote:
>> 
>> Trust me, my opinion is the same,  damn near any wall will stop the heat 
>> flow long enough to get the right heads to operate.  This is strictly a code 
>> question.  I'm OK and good at separating Code from opinion or even reality 
>> in many cases.  Reality is wall will stop the heads on the other side for an 
>> hour but Code seems to be silent.  OK when the unrated steel holding up wall 
>> falls in 15 minutes assuming the sprinkler don't actually operate reality is 
>> the 1 hour wall falls in 15 minutes. OK the valve is open, sprinklers 
>> operate and the wall never fails until the municipal water supply runs out 
>> so all this is moot in the real reality.  I sleep better following Code.
>> 
>> Chris 
>> 
>> -----Original Message-----
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of Brad Casterline
>> Sent: Tuesday, May 20, 2014 7:33 PM
>> To: [email protected]
>> Subject: Re: Area/Density Method and Walls
>> 
>> The reason I ask Chris is, the calculation method sprung Not from "how fast 
>> does an accidental fire get how hot", but "if we make the second piece inch 
>> and a quarter can we reduce the main size a notch or two, and still get the 
>> same water?" And I hear the first remote areas were round! I would consider 
>> any barrier to the fire-driven heat flow, rated or not.
>> 
>>> On May 20, 2014, at 7:17 PM, Brad Casterline <[email protected]> 
>>> wrote:
>>> 
>>> Good water or bad?
>>> 
>>>> On May 20, 2014, at 7:12 PM, "Cahill, Christopher" <[email protected]> 
>>>> wrote:
>>>> 
>>>> I can't believe I'm asking this question after all these years.  Anyway, 
>>>> swallowing pride and asking.
>>>> 
>>>> 2010 NFPA 13 strict Density/Area method 11.2.3.2 and 22.4.4.1.1.  Great 
>>>> big room being subdivided. Existing system with a new wall added between 
>>>> heads on a BL.  Contractor had to add a head on one side to preserve the 
>>>> existing spacing (area) of the heads.  Without head over 130 sq.ft.  I 
>>>> take the 1.2 ^.5 of the area and get 46.5' required along the BL.  
>>>> Original system lets say calc'd 5 heads on the BL.  But now in the same 
>>>> 46.5' there are 6 heads on the BL.  Do I ignore the wall and require a new 
>>>> calc?  What if the wall is rated 1 hour do I ignore it?
>>>> 
>>>> I looked all over and can't seem to find anything definitive. Room design 
>>>> is out so not a consideration.  22.4.4.1.1.1 simply says all the heads in 
>>>> the 46.5'.  I can't find anything that says either to count the wall as a 
>>>> break so measure 46.5' from the wall in each direction and still see if 
>>>> there are 5 head or ignore it and there are now 6 heads.  I find 11.1.2 
>>>> that clarifies to extend the density or not.  I don't think that's 
>>>> applicable exactly. The question is not about whether to extend the 
>>>> density on either side. Let's just say it's all OH.
>>>> 
>>>> It gets a little more complex as on the one side of the wall they cut a 
>>>> head in on the BL but on the other side there is a perpendicular new wall 
>>>> and they come off same BL and arm over to two more head so if I ignore the 
>>>> walls there are now 8 heads off the 1 BL.
>>>> 
>>>> Prefer a code section or written reference 'cuz this is going to be a big 
>>>> deal if we ignore the walls.  Ordinarily with unrated walls they are 
>>>> ignored in density/area (of course can't find that reference).  I think 
>>>> I'm getting tripped up with the rated portion? Or maybe I'm just tired????
>>>> 
>>>> Chris Cahill, PE*
>>>> Associate Fire Protection Engineer
>>>> Burns & McDonnell
>>>> Phone:  952.656.3652
>>>> Fax:  952.229.2923
>>>> [email protected]<mailto:[email protected]>
>>>> www.burnsmcd.com<http://www.burnsmcd.com/>
>>>> *Registered in: MN
>>>> 
>>>> 
>>>> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For
>>>> 
>>>> 
>>>> 
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to