I can't speak for all of the testing, but I know that when they were doing full 
scale testing on the first QR sprinklers, the pressures and flows were 
controlled by a computer. During the actual test the computer held the pressure 
and flow to 7 psi at 15 gpm and as each sprinkler activated the computer ramped 
up the flow and pressure to maintain the minimum operating conditions at each 
sprinkler. In most cases 4 - 5 sprinkler controlled the fire. In one case the 
computer got behind by about .5 seconds, in that test over 20 sprinklers were 
activated and they stopped the test. They reran the test with sprinklers from 
the same manufacturer and only 5 sprinklers activated. This was back in 90, 91 
and I'm not sure which testing facility it was at.

 Richard Mote
Rowe Sprinkler Systems Inc.