I only have a copy of 08' NEC 110.26, but according to that any elec. Panels
you need to be 6'-0" above, or clear the equipment, unless there is a
ceiling in the room. I don't know if that applies to telecom panels. The
only time I've been told I can't run through a telecom room is military
projects so it might be a UFC requirement.

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack
Sent: Thursday, May 29, 2014 8:18 AM
To: [email protected]
Subject: telecom rooms

Is there anything in any code/standard that prohibits sprinkler piping from
passing through telecom rooms?  I don't have access to the NEC right now.  I
can't locate anything in NFPA 13 that would prohibit it.

I am on a project where due to phasing, I have to run a branch line through
the telecom room to supply 2 sprinklers on the other side of it for this
phase.  The engineer says you can't do it. I thought I remember something in
the NEC saying that sprinkler piping was acceptable to pass through these
electric and telecom rooms.  I just can't run over panels.

-- 