NEC Article 110.26(F)(1)(a).

Dedicated Electrical Space. 
The space equal to the width and depth of the equipment and extending from
the floor to a height of 1.8 m (6 ft) above the equipment or to the
structural ceiling, whichever is lower, shall be dedicated to the electrical
installation. No piping, ducts, leak protection apparatus, or other
equipment foreign to the electrical installation shall be located in this
zone.

Exception:  
(a)     Suspended ceilings with removable panels shall be permitted within
the 1.8-m (6-ft) zone.  

(b)      Foreign Systems. The area above the dedicated space required by
110.26(F)(1)(a) shall be permitted to contain foreign systems, provided
protection is installed to avoid damage to the electrical equipment from
condensation, leaks, or breaks in such foreign systems.  

(c)      Sprinkler Protection. Sprinkler protection shall be permitted for
the dedicated space where the piping complies with this section.  

(d)      Suspended Ceilings. A dropped, suspended, or similar ceiling that
does not add strength to the building structure shall not be considered a
structural ceiling. 


Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack
Sent: Thursday, May 29, 2014 9:51 AM
To: [email protected]
Subject: Re: telecom rooms

That is exactly my thoughts as well. This is a 3D model project, so I am
clear of all panels and everything else.  This no pipe in these rooms is an
old hold over from decades ago that seems to be stuck in many people's
heads.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

On 5/29/2014 8:38 AM, [email protected] wrote:
> I'd tell the engineer to site the code section that prohibits the pipe
passing through. It's ridiculous but I have seen AHJ's interpret the thing
about "no unnecessary equipment" to mean the pipe can enter but not leave an
electrical equipment room. I don't think there is any code at all about pipe
in a telecom room.
> Ron F
>
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]] On Behalf Of 
> Jerry Van Kolken
> Sent: Thursday, May 29, 2014 8:29 AM
> To: [email protected]
> Subject: RE: telecom rooms
>
> I only have a copy of 08' NEC 110.26, but according to that any elec.
Panels you need to be 6'-0" above, or clear the equipment, unless there is a
ceiling in the room. I don't know if that applies to telecom panels. The
only time I've been told I can't run through a telecom room is military
projects so it might be a UFC requirement.
>
> Jerry Van Kolken
> Millennium Fire Protection
> (760) 722-2722
>
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]]
> On Behalf Of Travis Mack
> Sent: Thursday, May 29, 2014 8:18 AM
> To: [email protected]
> Subject: telecom rooms
>
> Is there anything in any code/standard that prohibits sprinkler piping
from passing through telecom rooms?  I don't have access to the NEC right
now.  I can't locate anything in NFPA 13 that would prohibit it.
>
> I am on a project where due to phasing, I have to run a branch line
through the telecom room to supply 2 sprinklers on the other side of it for
this phase.  The engineer says you can't do it. I thought I remember
something in the NEC saying that sprinkler piping was acceptable to pass
through these electric and telecom rooms.  I just can't run over panels.
>
> --
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to