There is no such restriction.  This is the same as those who believe it's 
dangerous to put sprinklers in electrical rooms.  Old wives tales and myth rule 
the minds of some.  

A telecom room is typically low voltage modem and other phone/internet 
equipment.  It is not an electrical room.

In the NEC with regards to electrical rooms (transformers, switch gear and 
other big stuff like that) the restrictions are that sprinkler piping must not 
be run within the Dedicated Electrical Space which is typically the space from 
the floor up to 6ft above electrical gear or to the structural ceiling 
(whichever is lower) and the depth of the gear from the wall for example.  

The other space in the NEC is referred to as the Working Space. This is the 
space directly in front of the equipment up to 6.5 ft in height.  Above that, 
sprinkler piping is permitted.  

But a telecom closet is of no consequence unless you have electrical panels, 
then just give them the space required and keep going.  

BTW: You can view the NEC and other NFPA Standards free of charge directly from 
the NFPA web site.  

 

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Thursday, May 29, 2014 11:18 AM
To: [email protected]
Subject: telecom rooms

Is there anything in any code/standard that prohibits sprinkler piping from 
passing through telecom rooms?  I don't have access to the NEC right now.  I 
can't locate anything in NFPA 13 that would prohibit it.

I am on a project where due to phasing, I have to run a branch line through the 
telecom room to supply 2 sprinklers on the other side of it for this phase.  
The engineer says you can't do it. I thought I remember something in the NEC 
saying that sprinkler piping was acceptable to pass through these electric and 
telecom rooms.  I just can't run over panels.

-- 
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to