Right.  I'm troubled by the statement "It does not appear that the tanks
will need to be anchored".  One of the very first things I was taught
about buried tanks was the quick calculation of the weight of concrete
vs. the buoyant force of water, in order to assure that the slab was of
sufficient mass to keep the tank from being pushed out of the ground in
case of an Act of God class event, such as flooding or water table
rising or ... whatever.   I would say that a civil and/or soils engineer
at least needs to at least evaluate the excavation, consider stability
of the edges, factor the fill (I've always used pea gravel and not
recompacted native fill), blah, blah, blah.    A structural engineer
along with the soils engineer should sign off on reinforcement of any
slab as well.   See  - you already have a dinner party.   A boring
dinner party, but still a party.

SML

 



-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Todd Williams
Sent: Thursday, June 12, 2014 8:47 AM
To: [email protected]
Subject: Re: Tank installation - NFPA 22 - 03 ed

What Ron said, unless you understand soil mechanics and have the test
data from this site guy. Each tank weighs 32000# plus the weight of the
tank. There is a lot to go wrong if it is not supported correctly. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


> On Jun 12, 2014, at 11:12 AM, "Martinez, Dewayne"
<[email protected]> wrote:
> 
> At my past companies there was never a civil involved besides telling 
> us the general area to locate the tanks.
> Is it really that complicated?  Basically they are burring a couple of

> concrete septic tanks and pitching the pipe down to the inlet at the 
> building.  I was never really too involved in
> the whole digging process.      
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of 
> rongreenman .
> Sent: Thursday, June 12, 2014 9:14 AM
> To: [email protected]
> Subject: Re: Tank installation - NFPA 22 - 03 ed
> 
> DeWayne,
> 
> There must be a civil involved. You might want to consult. This not 
> the type of conversation to start with, "... I was thinking...."
> 
> 
> On Thu, Jun 12, 2014 at 5:55 AM, Martinez, Dewayne < 
> [email protected]> wrote:
> 
>> We have to have 2 - 8000gal concrete suction tanks installed below 
>> grade and the GC was asking me how far apart to put the tanks and 
>> what
> 
>> kind of foundation will they need.  The tanks will be side by side 
>> and
> 
>> I was thinking having them about 2ft apart, any suggestions?  It 
>> looks
> 
>> like from CH 11 that I would need a compacted base with 3in of sand 
>> cushion on top for the tank foundation.  It does not appear that the 
>> tanks will need to be anchored.  Everything look good so far?
>> 
>> Thanks,
>> 
>> 
>> 
>> Dewayne
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
>> 
> 
> 
> 
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis 
> Bacon, essayist, philosopher, and statesman (1561-1626)
> 
> A problem well stated is a problem half solved. -Charles F. Kettering,

> inventor and engineer (1876-1958) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to