I see accidental fires, Sprinklered or not, going through three phases: erratic 
growth, somewhat steady burning, then some sort of decay. If you look at what 
might be the lowest water level in the tank over two hours would be you could 
get an idea of what the minimum pressures at the sprinklers would be.

> On Jun 12, 2014, at 9:01 PM, Brad Casterline <[email protected]> wrote:
> 
> Probably not since there is a difference between the total capacity and the 
> available head at any one instant in time?
> 
>> On Jun 12, 2014, at 8:40 PM, Karen Lesko <[email protected]> wrote:
>> 
>> When evaluating fire water supply to ensure there is a 2 hour supply, do I
>> have to take the head pressure loss of the fire water tank level drop into
>> account over the 2 hours?  The tank has makeup from wells that have normal
>> and back-up power, and the well makeup into the fire water tank equals the
>> output of the fire pump.
>> 
>> Thank you in advance,
>> 
>> Karen Lesko
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to