Referring to 13, 2002

15.1.2 states "Water supplies shall be capable of providing the required flow 
and pressure for the required duration as specified in Chapter 11, Chapter 12, 
and Chapter 13."

Then these chapters give various durations, starting from 30 minutes (light 
hazard) to as much as 3 hours (higher hazard). However, I have seen the two 
hour requirement being used for all types of occupancies and was wondering if 
this was a requirement in 13.

Tony 

----- Original Message -----
From: "Todd - Work" <[email protected]>
To: [email protected]
Sent: Wednesday, June 18, 2014 9:24:19 AM
Subject: Re: 2 hour fire water supply

Look up water supply duration in 13

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Jun 18, 2014, at 11:08 AM, Tony Silva <[email protected]> wrote:
> 
> Can anyone tell me from where the requirement for the two hour supply comes 
> from? Is it a code requirement? If so, which?
> 
> Thanks,
> 
> Tony 
> 
> ----- Original Message -----
> From: "Karen Lesko" <[email protected]>
> To: [email protected]
> Sent: Thursday, June 12, 2014 7:40:10 PM
> Subject: 2 hour fire water supply
> 
> When evaluating fire water supply to ensure there is a 2 hour supply, do I
> have to take the head pressure loss of the fire water tank level drop into
> account over the 2 hours?  The tank has makeup from wells that have normal
> and back-up power, and the well makeup into the fire water tank equals the
> output of the fire pump.
> 
> Thank you in advance,
> 
> Karen Lesko
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org