"5 gallon bucket and a stop watch"

Don't let the AHJ's hear of this.........


David Autry

Meininger Fire Protection Inc.
2521 W L St. Suite No.4
Lincoln, Ne 68522
Voice (402) 466-2616
Fax (402) 466-2617
[email protected]


-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Todd
Williams
Sent: Friday, June 20, 2014 11:02 AM
To: [email protected]
Subject: Re: to Pitot or not to Pitot?

5 gallon bucket and a stop watch

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


> On Jun 20, 2014, at 11:45 AM, "Brad Casterline"
<[email protected]> wrote:
>
> Whaaaa...? Where has 291 been all my life?!?
> I think I'll propose adding that if one has neither a gage OR a pitot,
> how to do it with a comb and a ruler.
>
> -----Original Message-----
> From: Parsley Consulting [mailto:[email protected]]
> Sent: Friday, June 20, 2014 10:20 AM
> To: [email protected]
> Subject: Re: to Pitot or not to Pitot?
>
> Roland,
>     Excellent description of what the intent of -291 describes in
> section 4.9.  As our mutual friend Joe Hankins used to say "Don't
> measure with a micrometer when you're going to cut with a chainsaw."
> *Ken Wagoner, SET
> *Parsley Consulting***
> *350 West 9th Avenue, Suite 206
> *Escondido, CA 92025-5053
> *****Phone 760.745.6181*
> Visit our website <http://www.parsleyconsulting.com/> ***
>> On 6/20/2014 8:04 AM, Roland Huggins wrote:
>> NFPA 291 says use a Pitot but IF a pitot is not available then a butt
> gauge will provide APPROXIMATELY the same results.  Unless one broke
> the bloody thing, if one doesn't have a pitot I suspect they shouldn't
> be out there.  Nonetheless, the velocity pressure in the discharge
> stream equals 100% of the pressure whereas the gauge pressure is just
> the normal pressure (that being total pressure minus velocity
> pressure) prior to the water outlet but it shouldn't be seeing the
> pressure loss associated with the water going through the outlet.
> Since the pitot reading is recommended to limit the velocity (not
> exceeding 30 psi on the pitot), it may not be a lot of difference.
> Combining this with the exacting precision associated with many pitot
> readings, it could be the TC felt it was close enough (like using hand
grenades).
>>
>> Roland
>>
>>
>> Roland Huggins, PE - VP Engineering
>> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves
Lives
>> Dallas, TX
>> http://www.firesprinkler.org
>>
>>
>>
>>
>>
>> On Jun 20, 2014, at 6:05 AM, Brad Casterline
>> <[email protected]>
> wrote:
>>
>>> Yesterday's flow test thread, along with talk of "because that is
>>> the way
> we
>>> have always done it" reminded me of something I have been wanting to
>>> post since last Christmas-- I was 'calculating' flow tests and
>>> looking for any info that might help and I discovered something that
>>> surprised me, that being NFPA 13 (2007) A.23.2.1 (2). For the
>>> flowing hydrant we can either attach a second gage or use a pitot. I
>>> have always used a pitot because
> that
>>> is the way the person who taught me had always done it.
>>>
>>> No question here, just thought I'd throw this out there on a Friday
> morning.
>>>
>>>
>>>
>>> thanks,
>>>
>>>
>>>
>>> Brad Casterline, NICET IV
>>>
>>> Fire Protection Division
>>>
>>>
>>>
>>> FSC, Inc.
>>>
>>> P: 913-722-3473
>>>
>>> [email protected]
>>>
>>> www.fsc-inc.com
>>>
>>>
>>>
>>> Engineering Solutions for the Built Environment
>>>
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>>
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to