You took the words out of my mouth figuratively speaking.   Design with
a computer, measure with a laser, mark with a paint pen, cut with an
axe.

If one is forced to take all their measurements at a single available
hydrant, the result may not be 100% accurate, but then a two-hydrant
test may not be either.  And our industry's "best practices" arguably
aren't the best at all.  How many people, when requesting or performing
a flow test or flow model, specify that the values be measured at peak
seasonal and peak day demands?   How much fluctuation does a given water
system or zone experience in a day/week/month/year?  How many of us
review those fluctuations and factor them into a flow test once it's
taken?    We need the flow data as a benchmark for calculations that
also have inherent susceptibility to variables we can't control; if you
have doubts about the precision of a flow test, you can always reduce it
by more than the widely applied 10% factor.   

How many people out there use a safety factor on a calculation that is
based on a fire pump performance curve?   If NFPA 20 and 25 both allow
for a 5% degradation of a pump's performance, shouldn't we be taking
5-10% off of pumps too?   The idea that we have to measure the water
supply using exponential factors that have to be expressed in scientific
notation is  ...  overkill.   I'm not advocating sloppiness by any
means, but if I had to choose between the results of a single hydrant
flow test or a model that has been verified to represent peak seasonal
and day demands and a two- or three-hydrant test that was taken at some
time on some day that was convenient because the traffic was light, I'll
go with the substantiated data every time, even if it isn't as
"accurate" as more widely accepted good practice.

SL




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Parsley Consulting
Sent: Friday, June 20, 2014 8:20 AM
To: [email protected]
Subject: Re: to Pitot or not to Pitot?

Roland,
     Excellent description of what the intent of -291 describes in
section 4.9.  As our mutual friend Joe Hankins used to say "Don't
measure with a micrometer when you're going to cut with a chainsaw."
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, CA 92025-5053
*****Phone 760.745.6181*
Visit our website <http://www.parsleyconsulting.com/> *** On 6/20/2014
8:04 AM, Roland Huggins wrote:
> NFPA 291 says use a Pitot but IF a pitot is not available then a butt
gauge will provide APPROXIMATELY the same results.  Unless one broke the
bloody thing, if one doesn't have a pitot I suspect they shouldn't be
out there.  Nonetheless, the velocity pressure in the discharge stream
equals 100% of the pressure whereas the gauge pressure is just the
normal pressure (that being total pressure minus velocity pressure)
prior to the water outlet but it shouldn't be seeing the pressure loss
associated with the water going through the outlet.  Since the pitot
reading is recommended to limit the velocity (not exceeding 30 psi on
the pitot), it may not be a lot of difference.  Combining this with the
exacting precision associated with many pitot readings, it could be the
TC felt it was close enough (like using hand grenades).
>
> Roland
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves
Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
>
>
> On Jun 20, 2014, at 6:05 AM, Brad Casterline <[email protected]>
wrote:
>
>> Yesterday's flow test thread, along with talk of "because that is the
way we
>> have always done it" reminded me of something I have been wanting to
post
>> since last Christmas-- I was 'calculating' flow tests and looking for
any
>> info that might help and I discovered something that surprised me,
that
>> being NFPA 13 (2007) A.23.2.1 (2). For the flowing hydrant we can
either
>> attach a second gage or use a pitot. I have always used a pitot
because that
>> is the way the person who taught me had always done it.
>>
>> No question here, just thought I'd throw this out there on a Friday
morning.
>>
>>
>>
>> thanks,
>>
>>
>>
>> Brad Casterline, NICET IV
>>
>> Fire Protection Division
>>
>>
>>
>> FSC, Inc.
>>
>> P: 913-722-3473
>>
>> [email protected]
>>
>> www.fsc-inc.com
>>
>>
>>
>> Engineering Solutions for the Built Environment
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
>
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to