Craig,

I don't see the "whole lot more" of CMSA you are referring to.  I am tied to 
the K16.8 because of storage height, storage configuration, expanded and 
non-expanded group A plastics, and idle wood pallets.  My alternate is 
0.65/2500, and I was trying to avoid that.

The Victaulic below is not CMSA so that doesn't help. I have been unable to get 
to Victaulic's website today.  Every attempt ends up at a Victaulic China 
website and wants me to translate. I see the Victaulic 25.2 ESFR refers to a 
16.8 CMSA, but I haven't found it on the Chinese website yet!

A "CMSA" search on the Reliable website only comes up with the N252 I listed 
below, not a 16.8 CMSA.

Scott
 
(763) 425-1001x12 Office
(612) 759-5556 Cell

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, June 23, 2014 3:43 PM
To: [email protected]
Subject: RE: CMSA Sprinkler Question

Victaulic lists a 16.8 ESFR
Reliable list a 16.8 CMSA

There are whole lot more CMSA sprinklers than just three if you're looking 
cross the different K-factors.

The internet is a wonderful tool for doing searches on information like this.  
;)

Are you tied to a 16.8 for any reason?


Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Scott A Futrell
Sent: Monday, June 23, 2014 4:13 PM
To: [email protected]
Subject: FW: CMSA Sprinkler Question

Okay.  Thanks John D. for pointing out that I wrote, "...the two below" and 
then listed three.

Let me try again.

I need a CMSA K16.8 sprinkler to meet specific criteria in NFPA 13, 2013, for a 
design project I am specifying.

Is Tyco the only manufacturer of a CMSA K16.8 sprinkler?

If not, who else has one?

Thanks and thanks John!

Scott
 
(763) 425-1001x12 Office
(612) 759-5556 Cell

-----Original Message-----
From: Scott A Futrell 
Sent: Monday, June 23, 2014 11:13 AM
To: '[email protected]'
Subject: CMSA Sprinkler Question

Forumites:

I need a CMSA K16.8 sprinkler to meet specific criteria in NFPA 13, 2013.

Are the only CMSA sprinklers available the two below?
Reliable, N252 EC - CMSA, RA0842
Tyco, Ultra K-17-231, TY7153
Viking, K19.6, VK592

Thanks!

Scott Futrell
 
(763) 425-1001x12 Office
(612) 759-5556 Cell

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to