Your Table in NFPA 13 only gives you one sprinkler selection, a 16.8K? Craig L. Prahl Fire Protection Group Lead CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29303 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected]
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Scott A Futrell Sent: Monday, June 23, 2014 5:17 PM To: [email protected] Subject: RE: CMSA Sprinkler Question Craig, I don't see the "whole lot more" of CMSA you are referring to. I am tied to the K16.8 because of storage height, storage configuration, expanded and non-expanded group A plastics, and idle wood pallets. My alternate is 0.65/2500, and I was trying to avoid that. The Victaulic below is not CMSA so that doesn't help. I have been unable to get to Victaulic's website today. Every attempt ends up at a Victaulic China website and wants me to translate. I see the Victaulic 25.2 ESFR refers to a 16.8 CMSA, but I haven't found it on the Chinese website yet! A "CMSA" search on the Reliable website only comes up with the N252 I listed below, not a 16.8 CMSA. Scott (763) 425-1001x12 Office (612) 759-5556 Cell -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Monday, June 23, 2014 3:43 PM To: [email protected] Subject: RE: CMSA Sprinkler Question Victaulic lists a 16.8 ESFR Reliable list a 16.8 CMSA There are whole lot more CMSA sprinklers than just three if you're looking cross the different K-factors. The internet is a wonderful tool for doing searches on information like this. ;) Are you tied to a 16.8 for any reason? Craig L. Prahl Fire Protection Group Lead CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29303 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Scott A Futrell Sent: Monday, June 23, 2014 4:13 PM To: [email protected] Subject: FW: CMSA Sprinkler Question Okay. Thanks John D. for pointing out that I wrote, "...the two below" and then listed three. Let me try again. I need a CMSA K16.8 sprinkler to meet specific criteria in NFPA 13, 2013, for a design project I am specifying. Is Tyco the only manufacturer of a CMSA K16.8 sprinkler? If not, who else has one? Thanks and thanks John! Scott (763) 425-1001x12 Office (612) 759-5556 Cell -----Original Message----- From: Scott A Futrell Sent: Monday, June 23, 2014 11:13 AM To: '[email protected]' Subject: CMSA Sprinkler Question Forumites: I need a CMSA K16.8 sprinkler to meet specific criteria in NFPA 13, 2013. Are the only CMSA sprinklers available the two below? Reliable, N252 EC - CMSA, RA0842 Tyco, Ultra K-17-231, TY7153 Viking, K19.6, VK592 Thanks! Scott Futrell (763) 425-1001x12 Office (612) 759-5556 Cell _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org