Yes, for my specific storage height, building height, nonexpanded group a in 
racks and also expanded, cartoned, in piles, and idle wood pallets.  Trying to 
protect all of those through all the applicable Tables, yes.  Palletized and 
solid pile exposed unexpanded and cartoned exposed table 15.3.1 really starts 
limiting you for the rest of the hazards.
Scott
 
(763) 425-1001x12 Office
(612) 759-5556 Cell

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, June 23, 2014 4:19 PM
To: [email protected]
Subject: RE: CMSA Sprinkler Question

Your Table in NFPA 13 only gives you one sprinkler selection, a 16.8K?

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Scott A Futrell
Sent: Monday, June 23, 2014 5:17 PM
To: [email protected]
Subject: RE: CMSA Sprinkler Question

Craig,

I don't see the "whole lot more" of CMSA you are referring to.  I am tied to 
the K16.8 because of storage height, storage configuration, expanded and 
non-expanded group A plastics, and idle wood pallets.  My alternate is 
0.65/2500, and I was trying to avoid that.

The Victaulic below is not CMSA so that doesn't help. I have been unable to get 
to Victaulic's website today.  Every attempt ends up at a Victaulic China 
website and wants me to translate. I see the Victaulic 25.2 ESFR refers to a 
16.8 CMSA, but I haven't found it on the Chinese website yet!

A "CMSA" search on the Reliable website only comes up with the N252 I listed 
below, not a 16.8 CMSA.

Scott
 
(763) 425-1001x12 Office
(612) 759-5556 Cell

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, June 23, 2014 3:43 PM
To: [email protected]
Subject: RE: CMSA Sprinkler Question

Victaulic lists a 16.8 ESFR
Reliable list a 16.8 CMSA

There are whole lot more CMSA sprinklers than just three if you're looking 
cross the different K-factors.

The internet is a wonderful tool for doing searches on information like this.  
;)

Are you tied to a 16.8 for any reason?


Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Scott A Futrell
Sent: Monday, June 23, 2014 4:13 PM
To: [email protected]
Subject: FW: CMSA Sprinkler Question

Okay.  Thanks John D. for pointing out that I wrote, "...the two below" and 
then listed three.

Let me try again.

I need a CMSA K16.8 sprinkler to meet specific criteria in NFPA 13, 2013, for a 
design project I am specifying.

Is Tyco the only manufacturer of a CMSA K16.8 sprinkler?

If not, who else has one?

Thanks and thanks John!

Scott
 
(763) 425-1001x12 Office
(612) 759-5556 Cell

-----Original Message-----
From: Scott A Futrell 
Sent: Monday, June 23, 2014 11:13 AM
To: '[email protected]'
Subject: CMSA Sprinkler Question

Forumites:

I need a CMSA K16.8 sprinkler to meet specific criteria in NFPA 13, 2013.

Are the only CMSA sprinklers available the two below?
Reliable, N252 EC - CMSA, RA0842
Tyco, Ultra K-17-231, TY7153
Viking, K19.6, VK592

Thanks!

Scott Futrell
 
(763) 425-1001x12 Office
(612) 759-5556 Cell

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to