Todd / Tim
        NFPA 1 provides information regarding reduction of fire flows in
those jurisdictions that have adopted this code.   Section 18.4.5.2 &
18.4.5.2.1 allow a reduction of 75% for an approved automatic sprinkler
system but not less than 1000 gpm and a structure utilizing Quick Response
sprinklers can be reduced to not less than 600 gpm.
        
        Dick Culver 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Todd - Work
Sent: Thursday, June 26, 2014 11:39 AM
To: [email protected]
Subject: Re: Water Supply Evaluation


I would probably make sense to have the Architect or his Engineer make the
call. There is an allowance in 1142 for the AHJ to decrease the required
volume for a sprinklered building. Is he/she taking this into consideration?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Jun 26, 2014, at 11:25 AM, "Tim Stone" <[email protected]> wrote:
> 
> Craig,
> 
> In this case I was hired by the Architect to design a Sprinkler system 
> for a brand new Church. The project is in a rural setting so fire pump 
> and tanks are being used. Is it reasonable for the AHJ to expect the 
> NICET certified designer to perform this duty or shouldn't this 
> responsibility fall back onto the Architect who in this case would be the
EOR?
> 
> Regards,
> G. Tim Stone
> 
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician Fire Protection Sprinkler 
> Design and Consulting Services
> 
>                 117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>                            [email protected]
> 
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]]
> On Behalf Of [email protected]
> Sent: Thursday, June 26, 2014 11:03 AM
> To: [email protected]
> Subject: RE: Water Supply Evaluation
> 
> Is your project a rural or suburban project?
> 
> Fire flow requirements should be identified by the EOR with direction 
> from the local or otherwise applicable fire authority.
> 
> I typically make a call to the local fire authority to find out what 
> method is used to determine fire flow.  There are several different 
> methods out there with requirements that vary greatly so guessing isn't a
wise move.
> 
> Once we know their approved method, we apply that info and determine 
> what is required to meet Code.  Sometimes that entails a tank and 
> pump, sometimes not.
> 
> Fire Flow is one thing that gets overlooked a lot in engineering 
> design.  We recently had one contractor telling an owner that the 
> requirements for fire flow were ridiculous and he's never had to do 
> that anywhere else.  I hope he doesn't do much design beyond 7-11 
> stores with his level of knowledge of the Codes.
> 
> Craig L. Prahl
> Fire Protection Group Lead
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]]
> On Behalf Of Steele, Andrew
> Sent: Thursday, June 26, 2014 10:47 AM
> To: [email protected]
> Subject: RE: Water Supply Evaluation
> 
> This most likely is from the International Fire Code, Chapter 5, Fire 
> Service Features, (G) Section 507 Fire Protection Water Supplies.
> Subsection 507.3 says "fire flow requirements for building or portions 
> of building and facilities shall be determined by an approved method".
> In Ohio, this has been adopted direct into the Ohio Administrative Code.
> I'm guessing any other jurisdiction using ICC are (or will) be doing the
> same.    
> 
> Typically the local Fire Marshal will help facilitate the evaluation 
> (to be conducted by a private fire protection/water utility 
> contractor) and will be the one to review/approve it.
> 
> Andrew Steele
> Dayton, OH
> (937) 333-4522
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of 
> Tim Stone
> Sent: Thursday, June 26, 2014 10:34 AM
> To: [email protected]
> Subject: Water Supply
> 
> 
> 
> Has anyone in other parts of the country run across this?
> 
> I just received a copy of a state fire marshal's review letter on a 
> new project in which they are asking that the (Water supply for 
> firefighting shall be evaluated and provided in accordance with NFPA
1142).
> 
> 
> 
> Who is responsible for this evaluation in your area?
> 
> 
> 
> Regards,
> 
> G. Tim Stone
> 
> 
> 
> G. Tim Stone Consulting, LLC
> 
> NICET Level III Engineering Technician
> 
> Fire Protection Sprinkler Design
> 
> and Consulting Services
> 
> 
> 
>                117 Old Stage Rd. - Essex Jct., VT. 05452
> 
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
> 
>                            <mailto:[email protected]> 
> [email protected]
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to