Todd / Tim
NFPA 1 provides information regarding reduction of fire flows in
those jurisdictions that have adopted this code. Section 18.4.5.2 &
18.4.5.2.1 allow a reduction of 75% for an approved automatic sprinkler
system but not less than 1000 gpm and a structure utilizing Quick Response
sprinklers can be reduced to not less than 600 gpm.
Dick Culver
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Todd - Work
Sent: Thursday, June 26, 2014 11:39 AM
To: [email protected]
Subject: Re: Water Supply Evaluation
I would probably make sense to have the Architect or his Engineer make the
call. There is an allowance in 1142 for the AHJ to decrease the required
volume for a sprinklered building. Is he/she taking this into consideration?
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
> On Jun 26, 2014, at 11:25 AM, "Tim Stone" <[email protected]> wrote:
>
> Craig,
>
> In this case I was hired by the Architect to design a Sprinkler system
> for a brand new Church. The project is in a rural setting so fire pump
> and tanks are being used. Is it reasonable for the AHJ to expect the
> NICET certified designer to perform this duty or shouldn't this
> responsibility fall back onto the Architect who in this case would be the
EOR?
>
> Regards,
> G. Tim Stone
>
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician Fire Protection Sprinkler
> Design and Consulting Services
>
> 117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343
> [email protected]
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]]
> On Behalf Of [email protected]
> Sent: Thursday, June 26, 2014 11:03 AM
> To: [email protected]
> Subject: RE: Water Supply Evaluation
>
> Is your project a rural or suburban project?
>
> Fire flow requirements should be identified by the EOR with direction
> from the local or otherwise applicable fire authority.
>
> I typically make a call to the local fire authority to find out what
> method is used to determine fire flow. There are several different
> methods out there with requirements that vary greatly so guessing isn't a
wise move.
>
> Once we know their approved method, we apply that info and determine
> what is required to meet Code. Sometimes that entails a tank and
> pump, sometimes not.
>
> Fire Flow is one thing that gets overlooked a lot in engineering
> design. We recently had one contractor telling an owner that the
> requirements for fire flow were ridiculous and he's never had to do
> that anywhere else. I hope he doesn't do much design beyond 7-11
> stores with his level of knowledge of the Codes.
>
> Craig L. Prahl
> Fire Protection Group Lead
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC 29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension 74102
> [email protected]
>
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]]
> On Behalf Of Steele, Andrew
> Sent: Thursday, June 26, 2014 10:47 AM
> To: [email protected]
> Subject: RE: Water Supply Evaluation
>
> This most likely is from the International Fire Code, Chapter 5, Fire
> Service Features, (G) Section 507 Fire Protection Water Supplies.
> Subsection 507.3 says "fire flow requirements for building or portions
> of building and facilities shall be determined by an approved method".
> In Ohio, this has been adopted direct into the Ohio Administrative Code.
> I'm guessing any other jurisdiction using ICC are (or will) be doing the
> same.
>
> Typically the local Fire Marshal will help facilitate the evaluation
> (to be conducted by a private fire protection/water utility
> contractor) and will be the one to review/approve it.
>
> Andrew Steele
> Dayton, OH
> (937) 333-4522
>
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of
> Tim Stone
> Sent: Thursday, June 26, 2014 10:34 AM
> To: [email protected]
> Subject: Water Supply
>
>
>
> Has anyone in other parts of the country run across this?
>
> I just received a copy of a state fire marshal's review letter on a
> new project in which they are asking that the (Water supply for
> firefighting shall be evaluated and provided in accordance with NFPA
1142).
>
>
>
> Who is responsible for this evaluation in your area?
>
>
>
> Regards,
>
> G. Tim Stone
>
>
>
> G. Tim Stone Consulting, LLC
>
> NICET Level III Engineering Technician
>
> Fire Protection Sprinkler Design
>
> and Consulting Services
>
>
>
> 117 Old Stage Rd. - Essex Jct., VT. 05452
>
> CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343
>
> <mailto:[email protected]>
> [email protected]
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org