Is area density appropriate for a booth?  Since you are required to
calculate the exhaust ducts with the paint spray booth, couldn't one argue
that it is a special design area or even room design (if its exterior, it
technically is separated from the building because of the exterior
self-closing doors and more than likely the appropriate rated walls)?   

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of IPA
Sent: Tuesday, July 22, 2014 3:53 PM
To: [email protected]
Subject: Paint Spray Booth OUTSIDE of Building

Applicable codes are NFPA 33 and 2013 ed. of NFPA 13:

I have a paint spray booth located completely outside of the main building
(by about 10 ft) but will take it's supply from the existing riser inside
the building. I'm wondering if I have to calculate according to the
provisions of 23.4.4.1.1.4 even though this system is not part of the
interior system? (unless you want to count the common supply - in this case
the riser.) _______________________________________________