Area/density is what '33 points you to - the area is the whole booth. The handbook material on the section I mentioned earlier (page 1007 AHJ FAQ) uses a paint booth as one of their examples for precisely this type of scenario with the exception that mine is completely outside the building. And that is my question - since this booth is completely outside the only attachment to the existing building is it's tap from the system riser. I think the case could be made to have a standalone calculation in this instance but wanted to see what the forum thinks.
On Tue, Jul 22, 2014 at 1:07 PM, Jeremy Frazier <[email protected]> wrote: > Is area density appropriate for a booth? Since you are required to > calculate the exhaust ducts with the paint spray booth, couldn't one argue > that it is a special design area or even room design (if its exterior, it > technically is separated from the building because of the exterior > self-closing doors and more than likely the appropriate rated walls)? > > -----Original Message----- > From: Sprinklerforum [mailto: > [email protected]] > On Behalf Of IPA > Sent: Tuesday, July 22, 2014 3:53 PM > To: [email protected] > Subject: Paint Spray Booth OUTSIDE of Building > > Applicable codes are NFPA 33 and 2013 ed. of NFPA 13: > > I have a paint spray booth located completely outside of the main building > (by about 10 ft) but will take it's supply from the existing riser inside > the building. I'm wondering if I have to calculate according to the > provisions of 23.4.4.1.1.4 even though this system is not part of the > interior system? (unless you want to count the common supply - in this case > the riser.) _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > ______________________________________________________________________ > This email has been scanned by the Symantec Email Security.cloud service. > For more information please visit http://www.symanteccloud.com > ______________________________________________________________________ > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org