If the paint spray booth is 10' or more from the building, I would agree.

John

This represents my personal opinion as a member of the Sprinkler System 
Discharge committee of NFPA 13, and does not imply the official position of the 
NFPA.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of IPA
Sent: Wednesday, July 23, 2014 10:02 AM
To: [email protected]
Subject: Re: Paint Spray Booth OUTSIDE of Building

Area/density is what '33 points you to - the area is the whole booth. The
handbook material on the section I mentioned earlier (page 1007 AHJ FAQ)
uses a paint booth as one of their examples for precisely this type of
scenario with the exception that mine is completely outside the building.
And that is my question - since this booth is completely outside the only
attachment to the existing building is it's tap from the system riser. I
think the case could be made to have a standalone calculation in this
instance but wanted to see what the forum thinks.




On Tue, Jul 22, 2014 at 1:07 PM, Jeremy Frazier <[email protected]>
wrote:

> Is area density appropriate for a booth?  Since you are required to
> calculate the exhaust ducts with the paint spray booth, couldn't one argue
> that it is a special design area or even room design (if its exterior, it
> technically is separated from the building because of the exterior
> self-closing doors and more than likely the appropriate rated walls)?
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]]
> On Behalf Of IPA
> Sent: Tuesday, July 22, 2014 3:53 PM
> To: [email protected]
> Subject: Paint Spray Booth OUTSIDE of Building
>
> Applicable codes are NFPA 33 and 2013 ed. of NFPA 13:
>
> I have a paint spray booth located completely outside of the main building
> (by about 10 ft) but will take it's supply from the existing riser inside
> the building. I'm wondering if I have to calculate according to the
> provisions of 23.4.4.1.1.4 even though this system is not part of the
> interior system? (unless you want to count the common supply - in this case
> the riser.) _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to