IBC Jerry.

On Thu, Aug 21, 2014 at 8:42 AM, <[email protected]> wrote:

> Good morning Ladies/Gentlemen:
>
> I do not know where < 20 sprinklers might be found in 25  (or any other
> standard) and/or why there would be such a stipulation in the  first
> place...That said: IF an overwhelming number of  failures attributed to
> sprinkler
> systems (all sizes) are due  to closed valves and/or inadequate water
> supplies,
> it seems 'logical' that, if a  sprinkler system has a water supply and/or
> control valve, those devices would  need to be check/tested/inspected,
> regardless of the number of sprinklers in the  system?? The number '20'
> has been
> bandied around for years as to adding that  number of heads to an existing
> system, plans submittals, whether a hydro was  required, FDC requirement,
> etc.
>
> In my professional (albeit humble) opinion, ALL fire sprinkler  systems
> need to be inspected/tested per NFPA-25 guidelines. I rather suspect our
> friends in the insurance industry would concur. In New Mexico, it is
> quarterly -
> it is statewide (commercial systems).
>
> Best to All-
>
> Jerry
> [email protected]_ (mailto:[email protected])
>
> Jerry D. Watts, SFPE
> President & Co-Founder
> ACCENT FIRE ENGINEERING INT'L. Ltd.*
> Santa Fe, New Mexico (a U.S. State)
> (800) 503.1961 nationwide
>
> *Founded 1991
>
>
>
> In a message dated 8/21/2014 9:29:26 A.M. Mountain Daylight Time,
> [email protected] writes:
>
> In  Seattle the rule was, and may still be but I haven't worked in industry
> for  some time, that a six head or less T.I. didn't require an inspection,
> but  that was local to Seattle.
>
>
> On Thu, Aug 21, 2014 at 5:11 AM, Greg  McGahan <[email protected]>
> wrote:
>
> > * NFPA #25.2.1.4*  says that modifications affecting less than 20
> sprinklers
> > does not  require hydrostatic testing...we regularly have inspections for
> 1
> > and  2 head mods...
> >
> >
> > Greg McGahan
> > Living Water Fire  Protection, LLC <http://www.livingwaterfp.com>
> > 1160 McKenzie  Road
> > Cantonment, FL 32533
> > 850-937-1850
> > fax  850-937-1852
> >
> >
> > On Wed, Aug 20, 2014 at 2:10 PM, Charles  Thurston <[email protected]>
> > wrote:
> >
> > > Hello  Sprinklerforum,
> > >
> > >   I have been told  verbally by an AHJ in the area that systems under
> 20
> > > heads do not  have to be inspected. He said it was in the code, But has
> > not
> >  > been able to pinpoint where.  I am unable to find that code
> reference,
> > > Anybody know where it would be?
> > >
> >  > --
> > > Best regards,
> > >  Charles      mailto:[email protected]
> > >
> > >  _______________________________________________
> > > Sprinklerforum  mailing list
> > > [email protected]
> >  >
> > >
> >
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >  >
> > _______________________________________________
> >  Sprinklerforum mailing list
> >  [email protected]
> >
> >
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering  Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA  98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700  (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS,  WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their  vocations. -Francis
> Bacon,
> essayist, philosopher, and statesman  (1561-1626)
>
> A problem well stated is a problem half solved. -Charles F.  Kettering,
> inventor and engineer  (1876-1958)
> _______________________________________________
> Sprinklerforum  mailing  list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to